An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull
out torque will occur. The rotor resistance per phase is 0.3
ohm and motor stalls at 650 rpm. The rotor frequency at
maximum torque point is
A 3.33% B 4.44%
C 5.55% D 6.66%
Answer / jay laruja
-slip at 650 rpm
120fs/p
= (120 x 50) / 8
= 750
slip = (Ns + Nr) / Ns = 0.133
fr = s x fs = 0.13 x 50 = 6.667%
there you go buddy ;)
Is This Answer Correct ? | 1 Yes | 0 No |
Why the wave trap is put in Y phse only in switchyard?why not in other phases?
What is the purpose of stand by earth fault protection for transformer ?
On a 10 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 65 AH). What Shall be the current rating of DC MCB ?
6 Answers RR, TNEB Tamil Nadu Electricity Board,
Why we use three phase world wide why not four phase or five phase being used?
what is the difference between electrical & electronics?
sir my exam is on 19/6/2013 under electrical branch pls send me sample aptitude questions as well as sample technical questions for jindal steel and power company
why celing fan is running in anti clock wise and table fan is running in clock wised?
why v/f ratio to maintain constant in speed control of induction motor?
why capacitors cant used in genset to maintain power factor..??
what's the difference between ATS and AMF...??pls answer me in detail with its working principle and construction also..
How to calculate ant test the burden of Current transformer
What is difference between miniture circuit breaker and module case circuit breaker up to 63Amp.