Why 66KV is step down to 11KV and then 433v, not directly
66KV to 433v ?
Answers were Sorted based on User's Feedback
Answer / 7anoter4
66 kV it is a transmission line. Distribution line-
connecting power transformer -it is usually 4-35 kV. A
small transformer- up to 3000 kVA -built for 66 kV will be
2-3 times more expensive- including breakers or special
high-voltage fuses. The maintenance is more expensive. A
transformer failure could produce a 66 kV line trip and so
a large number of consumers would remain without energy
supply.
The expensive transmission line connects large transformers
in safe conditions and from here cheaper distribution lines
will get close to the cheaper small transformer locations.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / niresh yadav
:+ As we know that ' from feraday first low when any conductor cut the flux more than flux linkage is more * so when primary side of transformer has 66 kv voltage so indused is high ! In comperision primary turns ratio secondary turns are very low when we change 66 kv to 433 volt than secendary are burns due to induction ! So we convert 66 kv to 11 kv first for protection.
Is This Answer Correct ? | 3 Yes | 3 No |
What it indicates by 25/41MVA on transformer?
How are calculated the aluminium busbar cross section area?
how can we change the rotating direction of single phase AC induction motors?
12 Answers Heubach Colour, L&T, MNM Jain Engineering College,
what is the value of combined earthing in general electrical circiut?
0 Answers Cathtect Engineering,
What is proportional controller?
A group of machines (wind turbines) connected with 33KV feeder and each machines are having individual VCB. The 33KV feeder connected with 110KV/33KV substation. The 33KV feeder tripped by over current at Substation and fault recorded at Substation as OC-R&Y phase. Same time the group of machines VCB tripped by over voltage, the fault recorded voltage was above 66KV by numerical Under/Over voltage relay. While grid drop time, this much of voltage hike is possible?
In a panel 2500A ACB is the incoming breaker then what is the size of the bus bar?
Can we use BS 6651 and BS EN 62305 standards for computer room lightning ptotection in substation?
can we choose current transformer secondary, to calculate residual flux in a power transformer, so as its saturation is close to the saturation level of power transformer?
What is LT? And specify the range of voltage?
why do select 11000v rubber mat even we use only 415Volts
1 Answers Saint Gobain, Tata Steel Limited,
What is the difference between Contactor and Circuit breaker ?