Why iron core transformers not used in high frequency
applications ?
Answers were Sorted based on User's Feedback
Answer / dinesh chaudhary
core losses are of two types i.e. hysteresis & eddy current
losse & hysteresis losses are directly proportional to the
frequency & eddy current losses are directly proportional
to the square of the frequency so, the losses will increase
that's why we cant use iron core transformer in high
frequency applications.
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / zohaib
iron core losses are directly proportional to frequency , greater frequency means greater iron core losses
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / dipankar
i think induced emf~phi.f, where phi=flux, and f=frequency.
to get a certain amount of induced emf for higher frequency
phi should have to be much lower value, and the required
iron core material should be of very high value, as for
lower flux value the flux density should be decreased and
required volume of the core for lower value of flux should
be increased, which is very undesirable for some
application like in airplane etc.Thats why we use air cored
transf. in place of iron cored transf. in high f.
| Is This Answer Correct ? | 1 Yes | 1 No |
What is the difference between tie bus and bus coupler?
a 650 KVA diesel generator is 1500 rpm, voltage is 415V n full load amps is 805 something,when are applied load more than 400 amps it's voltage is dropping, what is the reasons...?
What are various impedence in any machine
2 Answers Engineers India Limited, NTPC,
what is LA CT PT panel?
3 Answers Dwarikesh Sugar Industries, NTPC,
testing of transformer
Why glands not provided for XLPE cables
how to reduce power loss when the tranmission under long distance?
Draw the DOL starter and star delta starter drawing?
in alternator how we can give power to rotor ? its power is AC or DC ?
whenever any squirrel or a crow falls on the transformer input line then there is a big explosion and 440 volts of power is being discharged through the neutral line due to which appliances in off mode are also burned.we have earthing for the transformer as well as the bus bar chamber.why is it happening?
A rotor of an induction machine is delta connected. Now is there any necessacity to short the slip rings?
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)