230v 1 phase Phase and Neutral insert in Bulk water what happens.
Current will flow through the water. If the wires ar close
enough it will cause an overload. If they are far enough
apart they will heat the water and can make the water boil
between the wires.
This method has been used to load test DG's. 3 pointed
metal plates are fixed onto a triangle of wood and a phase
connected to each. When the plates are lowered into the
water current will flow through the water. The further the
plates are lowered the greater the current.
Note that this is very dangerous if great care is not taken
and all people are kept away from the water.
Is This Answer Correct ? | 2 Yes | 0 No |
what is relation between motor poles & motor current in 3 phase motor
HOW TO FIND THE PRIMARY AND SECONDARY OF TRANSFORMER(IN OFF CONDITION) USING MULTIMETER? IS IT POSSIBLE FIND BY SEEING RESISTANCE???
how do i work out the Amps of a incommer if i am running 1 37 KW motor and a 0,75 KW motor and some solinoids
How to select Main CB Rating for 187 KW Load?
what is kvarh? Please difine it With calculation
Three set (each phase contain 2 cable of 400 mmsq CU XLPE AWA) of single core cables are connected to 11 KV motor of 14 MW & the switch gear supplay is taken from 11kv feeder & this supplay taken from 275 KV substation. Problem is one pair cable(L3- 2 cable ) getting very hot & gland melted and damaged in switch gear side. the other two cable haven't any more hot(ambient temp only & L3 haveing 95- 100 Degree C. The same problem happened in 275 KV substation switch gear side also where the supply taken for 11 kv switch gear. But here L2 phese cable had problem. Why it is happening like this?. The cable having temperature different at different location from gland side inthe case of 11KV feeder of 275 kv substation. why ?
IS RTCC AND OLTC REQUIRED FOR 500 KVA 11KV/433V TRANSFORMER FOR AN INDUSTRY?
7 Answers IGCAR, TNEB Tamil Nadu Electricity Board,
Do any one know exacatly when the results for NHPC held on 8th march 09 for engineering trainees will be released ?. if so please post it, i'm eager to know it.
in an ac series circuit there are 30 bulbs are connected in a serial set.what will happen if one bulb is fused and we removed the bulb and reconnect with the remaining bulbs? (29 bulbs). will the brightness of other bulbs increase or not?
what is conductor constant of raccun conductor
0 Answers CSPDCL-Chhattisgarh State Power Distribution Company Limited,
For refrigerators the motor current is raised beyond its rating on both conditions when the voltage of the system is more(say 270v) than the rated voltage(220v) as well as when the voltage of system is less(say 160v) than normal voltageof 220v, why explain?
0 Answers Electrical Tech, UPSE,
A system absorbs 100 k J of heat and the increase in its internal energy is 100 kJ; the work done is