i have a dp tx range is 5000mmwc. in which calibration i use in a open tank.1.5*3.5*2.5 mtr.for level msmnt. what is the calculation.
Answers were Sorted based on User's Feedback
Answer / raj
Open tank level calculation = tank hight * density
Example for
3 meter tank hight
Process liquid for disel density 0.7
So calculation
3 * 0.7
2.1 meter
LRV. O
URU 2.1 meter if you wand change to mmh2o the unite
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / nitin sompura
See as per your data open tank height is 2.5 mtr
(2500mm).zero and 100% level if we consider as per your
tank and we suppose no safety margin for overflow as well
as for zero level for the pump, as you have not mentioned
clearly,
so according to you please keep your LP of DPT in
atmosphere, and HP point connect to the bottom of tank,and
if we consider tank of water then LRV:0.0mmWC,URL:2500 mmwc.
as per your medium you consider density.
| Is This Answer Correct ? | 7 Yes | 1 No |
how to given power supply of any type two wire transmitter in field?
How to control flow variations in magnetic flow maters..... When i will provide proper earthing?
draw the block diagram of a level transmitter ?
0 Answers Hira Group, Samsung,
What is calibration?
Can i convert 230v ac to 24v dc by using a relay?Instead of Smps is it possible? What is relay logic in plc ?? How it works?
How can one improve linearity of an RTD based temperature measurement system?
What is the cv of a control valve?
what is the difference between transmitter and converters?
Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer
what is the operation philosophy of proximity velocity sensor
How to calibrate capillary type level transmitter
Can we calibrate an actuator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)