Answer / raj
Open tank level calculation = tank hight * density
Example for
3 meter tank hight
Process liquid for disel density 0.7
So calculation
3 * 0.7
2.1 meter
LRV. O
URU 2.1 meter if you wand change to mmh2o the unite
Is This Answer Correct ? | 11 Yes | 1 No |
Answer / nitin sompura
See as per your data open tank height is 2.5 mtr
(2500mm).zero and 100% level if we consider as per your
tank and we suppose no safety margin for overflow as well
as for zero level for the pump, as you have not mentioned
clearly,
so according to you please keep your LP of DPT in
atmosphere, and HP point connect to the bottom of tank,and
if we consider tank of water then LRV:0.0mmWC,URL:2500 mmwc.
as per your medium you consider density.
Is This Answer Correct ? | 7 Yes | 1 No |
what do u mean by compensating?in power plant where are compensating done?how level , flow compensated?
how can we measure the pressure in underground cooling water pipeline by using pressure transmitter?what about the tapping position?
Why we use 250 ohm resistor in series with HART protocol communication?
13 Answers Chemtrols, Instec, Sabic,
Explain why use mmwc unit?
god evening sir i am studying m.sc(tech)electronics &instrumention.am i elegible to all industies
what is the thermocuple compensation circuit
what is differential pressure transmitter and transducer? how to work?
what do you know about Foundation Fieldbus?
Why 4ma - 20ma signal used in instrumentation??
in rotark mov in display err msg showing how to remove the error
what is the primary sensing element in flow or pressureand level transmitter?
We are used CENTUM CS3000 of YOKOGAWA. please tell me how to simulate wihtout FCS and vnet.