I have flow transmiter DP range is 0 to
5000mmwc,(convert) Display to be show in
m3/Hr.
Answers were Sorted based on User's Feedback
Answer / sajid ali khan
Dear the Flow range is not just a function of the flow
transmitter. It is function of the Flow Element, that can
be an Orifice or a venturi, etc.
You have to know the Flow calculations and then calculate
the relationship of dp vs flow
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sivaram
Dear bro.In flow calculation Need Design DP and Q Parameters,Then configure range DP ,out put function Sq root display range configure Given Q,Simple you will get Exact
flow
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / kirubakaran
example:
50% range =squareroot of(d.p/max-min)
50/100 = square root of(dp/5000-0)
take square on both side
2500*5000/10000= d.p(differential pressure)
1250mmwc= d.p
similiarly find 0%,25%,75%,100% this is for square root output
pls see range in dcs example 0-50ton
then put corresponding value
range o/p(ma) mmwc tons
0% 4 0 0
25% 8 312.5 12.5
50% 12 1250 25
75% 16 2812.5 37.5
100% 20 5000 50
if u feel correct means follow this
| Is This Answer Correct ? | 3 Yes | 6 No |
What is the meaning of the term "g force"?
3 Answers Reliance, Saint Gobain, Thermax,
What is 3 element control system
WHAT IS THE Differance b/w on/off & pid control valve?
What is shriking and swell effect for a boiler ?
WHAT IS THE MAIN WORKING OF BOILER.
what are the diff. in servo and regulatory control?
In close vessel/ drum why we use d.p. transmitter of -ve range i.e. (-)500 to 0 mmwc.
1)How many tpes of vibration probe and how many tpyes of vibration. 2)how we can calibrate a vibration probe with tk3 3)what is RMS value in vibration measuring application and how we calculate it.
Why boiler chimney area oxyden sensor fixing?
In which principle Woodward Governor 505 work in power plant? What are the input of Woodward governor 505
What is the use of single seated valve?
in the pipe line if the control valve fails to respond to controller action,by what means we can stop the flow in the pipe line ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)