What is cold junction compensation in thermocouples? How is
it achieved?
Answers were Sorted based on User's Feedback
Answer / guest
A thermocouple measurement involves two thermocouples, one
at hot junction and another, a cold junction, at 0degC.
Maintaining this cold junction at 0 degC is cumbersome, and
it is easier if it can be at room temperature. The
indicated temperature will be lesser by "room temperature
value", and if room temperature varies, then the indicated
temperature also varies. Measures to counteract these
errors is called cold junction compensation. When cold
junction temperature increases, the voltage from
thermocouple decreases. If an equivalent voltage is added
to this, then cold junction errors can be removed.One can
monitor this cold junction (near the terminals where the
thermocouples get connected to copper wires of indicator)
using another sensor, and add an equivalent voltage to
thermocouple voltage to compensate for changes in cold
junction. Alternatively, the ambient temperature measured
can be added to temperature computed from thermocouple
voltage to get CJC.
Is This Answer Correct ? | 18 Yes | 2 No |
TC works on the principle of SEEBACK's Effect, which states
the the temperature difference is directly proportional to
induced emf, when two dissimilar metals are twisted together
and heated at end.
its equation states,
hot junction - cold junction = induced emf.
its means hot junction is the temperature measured..
cold junction means the ambient temperature unlessly
considering the compensation. we have keep the cold junction
as constant by giving a constant hot source or ice bath. so
that its easy to find the hot junction values.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / guest
cold jn.compensation is achieved by introducing a 3 junction
called compensating jn.which does not allow the temperature of
cold jn.to rise above 1 degree celcius .
Is This Answer Correct ? | 0 Yes | 0 No |
Open ended through we received TC output as mv
Is This Answer Correct ? | 0 Yes | 4 No |
How to measure the dust in chimney(spm)?
In VVVF DRIVES VOLTAGE IS ALSO VARY WITH THE FREQUENCY. HOW? WHAT IS THE DIRECT FORMULA RELATING THESE TWO.
1 bar is equal to how many pound per square inch(psi)?
what is difference between E/P positioner and I/P positioner. Why E/P fixed in below actuator and why I/P fixed in other place
what are level of automation & how these are distinguished ?
what are the problem's will accure in dcs or plc hadware and what are the solution for it?
Related to control system, What is difference between 4-20 mA active & 4-20 mA pasive signal.
WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD
In the field and in the control room different power supplies if used How to handle the ground
what is isolation Transformer???...
What is the procedure of calibration of Load cell?
Instrumentation Safe Guarding test. How to determine the interval time of the test. eg:Halfyearly,Every year,Every three years etc.