Answer / rajen thakkar
Hipot test is used to test the cable for Its more than
rated voltage level for which it is designed.so, for 11KV
cable 19KV DC is applied for 1 Minute to R&Y,Y&B,B&R lead
of cable one by one & armoring is connected to earth. 11KV
Cable should withstand this voltage.If cable insulation is
weak so it will breakdown at this higher votage
level.Before & After the Hipot test cable meggering should
be done By 5Kv Megger.
| Is This Answer Correct ? | 19 Yes | 2 No |
Answer / prabhu krishna
hipot test is used to test the cable for Its more than
rated voltage level for which it is designed.so, for 11KV
cable 19KV DC is applied for 1 Minute to R&Y,Y&B,B&R lead
of cable one by one & armoring is connected to earth. 11KV
Cable should withstand this voltage.If cable insulation is
weak so it will breakdown at this higher votage
level.Before & After the Hipot test cable meggering should
be done By 5Kv Megger.
| Is This Answer Correct ? | 11 Yes | 1 No |
what is the value of the earth resistance in mositure place
make control wire diagram of start and stop a function with a single push button
When alarm is activated in buccholz relay in transformer
resistance switching is used in case of- ? a. air blast CB b. bulk oil CB c. minimum oil CB d. all types of CB
Please, if 1kw is equal to 1.25kva; how then do I know how many kva in 7.5kw?
what is relation between torque and speed / rpm?
What are the disadvantages of LT AVR over HT AVR?
1 Answers APTransco, Jindal, TNEB Tamil Nadu Electricity Board,
Why dry type cast resin transformers tap link blast in HV side while power shut down times on load?
What is the tolerence limit between neutral and earth in 230 V AC System?
how to determine motor size for a fan application?
How does frequency affect KVA rating of a transformer? If a 500 kva, 500 to 250 v, 60 hz t/f used in Canada is to be operated on 50 hz in Europe frequency then how will its KVA rating change? a-increase b-decrease c-remains same
how to calculate power loss cost of aluminium conductor and copper conductor?500v,100A,68mm area squre busbar.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)