How to conduct a Hipot test on a 11KV cable?
Answers were Sorted based on User's Feedback
Answer / rajen thakkar
Hipot test is used to test the cable for Its more than
rated voltage level for which it is designed.so, for 11KV
cable 19KV DC is applied for 1 Minute to R&Y,Y&B,B&R lead
of cable one by one & armoring is connected to earth. 11KV
Cable should withstand this voltage.If cable insulation is
weak so it will breakdown at this higher votage
level.Before & After the Hipot test cable meggering should
be done By 5Kv Megger.
| Is This Answer Correct ? | 19 Yes | 2 No |
Answer / prabhu krishna
hipot test is used to test the cable for Its more than
rated voltage level for which it is designed.so, for 11KV
cable 19KV DC is applied for 1 Minute to R&Y,Y&B,B&R lead
of cable one by one & armoring is connected to earth. 11KV
Cable should withstand this voltage.If cable insulation is
weak so it will breakdown at this higher votage
level.Before & After the Hipot test cable meggering should
be done By 5Kv Megger.
| Is This Answer Correct ? | 11 Yes | 1 No |
a 3 phase slip ring induction motor is wound for 4 poles on stator and 6 poles on rotor; when 3 phase balanced voltage source at 50 hz is applied to motor it will run at a)1500rpm b)1000rpm c)750 rpm d)zero rpm
13 Answers Essar, PSPCL, PSTCL,
What is the difference between AC and DC injection methods for rotor earth fault protection
0 Answers Asian Alliance Insurance, NBVL,
cable armor
How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)
9 Answers Career Excellent Sdn Bhd, Neona, Northern Max Engineering, Sps Renewables, Terasaki, UEM,
hi all i like to know vat is power plot in control systems also i want to know abt latest trends in electrical & electronics
how are reversing the direction of rotation of dc motor
Where the excitation is given either stator or rotor in actually in power plants?
electrical ques
To attain a powerfactor more than .95, how much kvr should we use for 100 HP of current
4 Answers Bhel, Scooters India,
How to select earthing strip for 100kw induction motor ?
why use generator Earthing/Graunding.
Why we are putting off the APFC(automatic power factor control) panel while the generator is running?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)