How to conduct a Hipot test on a 11KV cable?
Answers were Sorted based on User's Feedback
Answer / rajen thakkar
Hipot test is used to test the cable for Its more than
rated voltage level for which it is designed.so, for 11KV
cable 19KV DC is applied for 1 Minute to R&Y,Y&B,B&R lead
of cable one by one & armoring is connected to earth. 11KV
Cable should withstand this voltage.If cable insulation is
weak so it will breakdown at this higher votage
level.Before & After the Hipot test cable meggering should
be done By 5Kv Megger.
Is This Answer Correct ? | 19 Yes | 2 No |
Answer / prabhu krishna
hipot test is used to test the cable for Its more than
rated voltage level for which it is designed.so, for 11KV
cable 19KV DC is applied for 1 Minute to R&Y,Y&B,B&R lead
of cable one by one & armoring is connected to earth. 11KV
Cable should withstand this voltage.If cable insulation is
weak so it will breakdown at this higher votage
level.Before & After the Hipot test cable meggering should
be done By 5Kv Megger.
Is This Answer Correct ? | 11 Yes | 1 No |
What is transformer break down voltage.And what is flash oil flash point.
why transmission line towers are longer than communication line towers?
how much load should be given on 5 mva transformer
7 Answers NTPC, OHPC, Power Grid,
How to set the relay,,??
0 Answers Megatron Solutions, Nestle,
ABOUT AC GENARETORS AND MAINTANANCE AND TYPES OF GENARETORS
How many types of Transformer testing..
How would you supply a single house hold load from a 3-phase supply coming out of a sub-station?
how to calculate the distance relay faulty zone?pls explain?
why grid failure happens?
what is the working of air compressor.
why rotor winding in induction motor is not earthed. normally we uses star winding in rotor .why?
3 Answers Anglo Platinum, TATA,
If mutual flux is 1.2wb & power factor is 0.8 lag , then what is the Useful flux of a transformer?