Answer / shaik
First of all the voltage ratings given in the question might
be wrong. But the basic rule for calc. the ampacity is to
first find out the current..
Power/ Volts = Amp.
Then the ampacity of the conductor is choosen by taking 125%
of the current.
Here if i consider voltage of this tranformer to be 22/.433
kv. then on primary side the busbar capacity has to be,
1000x1000/22x1000 =45.45 A
45.45x 1.25=56.81 Amps.
Therefore the busbar capacity on primary side should not be
less than 60 Amps.
Similarly, secondary side is calc.
| Is This Answer Correct ? | 5 Yes | 4 No |
THE lv BUS IS DESIGNED FOE 25% OVERLOAD. 1.25 X In. Select
the nearest value as per standards manufacturer,.If you
exact your figures, supplier quote high price.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is an Air COmpressor
HRC fuse provide best protection against
What is marx circuit?
what is the meaning of impedance protected in instrument cooling fan
Why we are using only Dyn11 tranformer in distribution system but not using a Dyn1 in distributing system?why not and advantage and disadvantage in both
There is no such thing as a Generator. All power generating devices are Alternator since both generate alternating current since this is the only way electrical power can be generated. In "generators" the alternating current is converted into DC inside the housing of the "generator" in order to give out DC Do you agree? If not please educate me. How else is DC generated if not like above?
What is the advantage of AC supply?
hello! can anyone explain to me how a 3 speeds table fan work? what are the factors that are controlling the speed of a normal table fan? Is it by varying the voltage or changing the magnetic field? would appreciate your reply :) thx in advance.
What is the Load Capacity of Panther conductor (0.2) and dog conductor (0.1)
What is Instantaneous Earth fault relay,how will work
Why AC current leads voltage in capacitor and how?
I am an electrical engineer, I found variation in KWH between DG and EB for Same load for same duration, can any one help me why this variation arises?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)