how to calculate busbar capacity for 1000Kva transformer having22/.433V
Answers were Sorted based on User's Feedback
Answer / shaik
First of all the voltage ratings given in the question might
be wrong. But the basic rule for calc. the ampacity is to
first find out the current..
Power/ Volts = Amp.
Then the ampacity of the conductor is choosen by taking 125%
of the current.
Here if i consider voltage of this tranformer to be 22/.433
kv. then on primary side the busbar capacity has to be,
1000x1000/22x1000 =45.45 A
45.45x 1.25=56.81 Amps.
Therefore the busbar capacity on primary side should not be
less than 60 Amps.
Similarly, secondary side is calc.
Is This Answer Correct ? | 5 Yes | 4 No |
THE lv BUS IS DESIGNED FOE 25% OVERLOAD. 1.25 X In. Select
the nearest value as per standards manufacturer,.If you
exact your figures, supplier quote high price.
Is This Answer Correct ? | 0 Yes | 0 No |
What is the deference between earth fault & earth leakage
What is meant by derating factor?
what is maximum or Threshold value of current 7 voltage that a common man can withstand
what is different the DOL Starter and Star Delta STARTER
Classify drilling machines.
What is meant by locking of rotor in synchronous motor? Explain me locking in detail?
WHAT IS THE PARTIAL DISCHARGE TEST?
what is distribution board?
What is HVAC, PLS SEND DETAIL OF hvac.
What is the need for checking knee point voltage for CT's?
What is pi controller?
What is the stander resistance value between the neutral and earth?
10 Answers Crossdomain, Sepco,