what happen if rotor earth fault in AVR system?
Nothing happen. DC ground fault alarm persists. Generator
works as usaual.a single dc earth fault will not damage the
device.Just annouces there is weak insulation, trouble
shoot it. rotor is a dc circuit.
Do you mean DC circuit earth fault in avr
caabinet,slipring.
AVR means automatic voltage regulation -i.e when generator
voltage is high or low ,it corrects the filed current and
correct the voltage.
Now if there is a rotor earth fault, the AVR maintains the
voltage but there is current leaking. rotor fault should be
conveys through the air gap or oil film to ground. It is
detected by by a separat rotor earth fault detector known
as singlerotor earth fault. This single rotor must become
double rotor earth fault .Then there is circulating current
flowing and completes grund circuit , till the double earth
fault relay annuciate and isolate the generator.
| Is This Answer Correct ? | 2 Yes | 0 No |
Transformer Specification say 66/11KV, 23/27/35MVA OFDAN,what is OFDAN? we know ONAN,ONAF or OFAF
Is there a possibility to use such a treshold voltage for the NMOS part of a CMOS circuit that during the switching it will start conducting only after the PMOS part will be already closed, by this eliminating the leakedge current? Please note, I'm not asking about the well bias in standby mode, but about the "antileakedge" measures during normal operation.
why transformer are rated in kva.
List few applications of d.c series motor?
whats the application of voltage regulation? and whats the voltage regulation's device?
How to test Power Transfomer vector group in the field?
What does “battery of 180 AMP HOUR” mean to you?
why AC signals are represented by sinusoidal waveform?WHY other waveforms not used for representation
what is the difference between a hooter and a mcp
How is a 100 MVA transformer cooled?
how hazordious area is classified at an oil & gas plant and categorise suitable class of electric equipment in that area like induction motors, LCS, Lighting Fixtures Fluerescent/Flood lights Mercury& sodium lights, J.Bs, Power Cables etc
How to calculate no of Lighning arrestors are required for protecting 50mX 50m*20m cubical building and locations of LA?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)