what happen if rotor earth fault in AVR system?
Nothing happen. DC ground fault alarm persists. Generator
works as usaual.a single dc earth fault will not damage the
device.Just annouces there is weak insulation, trouble
shoot it. rotor is a dc circuit.
Do you mean DC circuit earth fault in avr
caabinet,slipring.
AVR means automatic voltage regulation -i.e when generator
voltage is high or low ,it corrects the filed current and
correct the voltage.
Now if there is a rotor earth fault, the AVR maintains the
voltage but there is current leaking. rotor fault should be
conveys through the air gap or oil film to ground. It is
detected by by a separat rotor earth fault detector known
as singlerotor earth fault. This single rotor must become
double rotor earth fault .Then there is circulating current
flowing and completes grund circuit , till the double earth
fault relay annuciate and isolate the generator.
Is This Answer Correct ? | 2 Yes | 0 No |
how to calculate the minimum permissible limts of insulation resistance of switchyard equipments
why are installed water leakage detection system data centers & server rooms
How can you calculate the size of the down conductor cable for the lightning protection system. Is 70mm2 cable can replace 95mm 2 bare copper cable when the copper tape size is 25Wx3 thk mm.
what is the design voltage for 6.6KV 2000 KVAR HT capacitor?
explain the f=np/120 this equ.how to come 120
3 Answers Jayaswal Neco Industries,
what is Distance protection & how did it work
why we use bare wire in high tension power instead of using insulated wire?
Define norton equivalent circuit?
function of apfc pannel
Compare salient pole and Hndrical rotor machines.
how regenerative breaking is done in electrical traction
CTs Ratio