what happen if rotor earth fault in AVR system?
Nothing happen. DC ground fault alarm persists. Generator
works as usaual.a single dc earth fault will not damage the
device.Just annouces there is weak insulation, trouble
shoot it. rotor is a dc circuit.
Do you mean DC circuit earth fault in avr
caabinet,slipring.
AVR means automatic voltage regulation -i.e when generator
voltage is high or low ,it corrects the filed current and
correct the voltage.
Now if there is a rotor earth fault, the AVR maintains the
voltage but there is current leaking. rotor fault should be
conveys through the air gap or oil film to ground. It is
detected by by a separat rotor earth fault detector known
as singlerotor earth fault. This single rotor must become
double rotor earth fault .Then there is circulating current
flowing and completes grund circuit , till the double earth
fault relay annuciate and isolate the generator.
Is This Answer Correct ? | 2 Yes | 0 No |
Explain what is use of lockout relay in ht voltage?
what is RR number Abbreviation energy meter
WHAT HAPPENS IF STARTER OF A FLUROSCENT LAMP IS SHORT CIRCUITED AND WE PUT THE SUPPLY ON?
Why power factor does not occur in DG set ?
What is Procedure the procedure to select CT's & PT's in 66kV and above substation?
3 Answers Infotech, Vijai Electricals,
how will calculate the safe starting current of 3-phase squirrel cage induction motor?
Cb closed condition if there is a tcs fail whether cb will trip or not
DGs fuel and lube oil filters are not equal to one another.Why it is so.For example one MTU enginee fuel filter is one and lube oil filter-02nos other DGs are more.Please explain
What is rated value? is it phase values or line values?
how to calculate the multiplication factor in HT incomer trivector meters
9 Answers Dalkia, Getco, Gujarat Energy Transmission Corporation Limited GETCO,
Earth has zero potential then what would be the neutral potential ?
which transmission is cheaper ac or dc?