WHICH SUPPLY IS BETTER FOR 4 MW LOAD.
1)TO TAKE NEARER AVAILABLE 11 KV SUPPLY OR
2)TO TAKE 33 KV SUPPLY WHICH IS AVAILABLE AT 10 KM DISTANCE
BY INVESTING NEARLY 50-60 LACKHS
Availing supply from nearby 11 KV line ,does not make it a dedicated supply as there are many dist trs on it and VR may exceed the limit for 4 MW. You can expect frequent power failures . Reconductoring may also be necessitated
| Is This Answer Correct ? | 0 Yes | 0 No |
Which type of transformer used in lighting load?
What is nichols chart?
While HT line put on to activate ACB in low tention panel VCB tripping instantly.why it happens
can induction motor becomes as a generator. if yes how it is possible. if there is a squirrel cage rotor.
Which motor runs on both ac and ac? a) dc series motor b) reluctance motor
How convergengr of nr method is not dependent on selection of slack bus and how gauss siedel method depends?
How to connect the earthing in aircraft?
WHAT TYPES OF OIL(STRUCTURE) ARE USED IN POWER TRANSFORMER INSULATION?
can u tell the difference between star-star transformer and delta to delta transformer.
Re: What do you mean by Power factor of a generator? Power factor purely depends on the load (wether inductive, reactive or unity) then what does the Power factor mentioned on the generator nameplate means?
I Have 3 Phase 10 KW AC Alternator i found one phase weak, so what will be the reason & what action shouls i take to rectify the same.
What is the difference between online and offline UPS
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)