How can I make calculation for Install level transmitter
(DP) for open tank and cloes tank?
Answer / mnb
For open tank you just connect HP side to the bottom of the tank and vent LP side to the atmosphere.
Head pressure becomes liquid level .URV=Height*specific gravity (H*SG) and LRV =0.
For closed tank, use dry leg for non condensate liquids and use wet leg for condensate liquids.
Dry leg-connect HP side to bottom and LP side to top of the tank. LRV =0, URV= H*SG.
No need to bother about pressure inside the tank because it acts upon both sides equally.
Wet leg- connect Hp side to lower tapping and LP side to upper tapping and fill the Lp side with process liquid.
LRV=h2*sg
URV= h1*sg-h2*sg.
h1= level of liquid at HP side
h2= level of liquid at LP side.
Is This Answer Correct ? | 1 Yes | 0 No |
Why do we use triad cable for RTD to Temp.transmitter connection? Why we don't use 3 core cable?
1 Answers Process Control Technologies,
waht is difference between pressure transmitter and transuducer
In E&I diagram what is the meaning of rectangular box and circular box
Explain about SOURCING & SINKING concepts in PLC to field sensor wiring ?
what is easiest way to read STL language in PLC?
How can we measure the level of a closed system like drum
WE Know that different supply voltage of solenoid valve like 24,110,220 etc..how we check the solenoid supply is 24v or 220 NOTE: No specification at device.
I am a instrument technician. recently i attend interview and face one of question for DP transmitter ,the client asking about the calibration of DP transmitter ,am answer the calibration procedure, they will ask one more question. why open LP side in atmosphere? i did not answer that question. so please help me and explain the particular question. Dear firends waiting for your valuable replay
3 Answers Qatar Petroleums, Samsung,
in natural gas indirect water bath heater,how to prevent the problem of backfire from firetube during ignition...becoz of this backfire performance of wbh is going low.
what is the equation for gas flowmetering? whic includes gas flow, pressure, and temperature.
difference b/w single acting and double acting actuator by using application only?
what is the difference b/w wet leg & dry leg level method