Minimum spacing of 2-
bars in column, beam,
slab
Answers were Sorted based on User's Feedback
Answer / mayank jain
Minimum Distance Between Individual Bars
main reinforcing bars shall usually be not-less
than the greatest of the following:
The following shall apply for spacing of bars:
a)The horizontal distance between two parallel
Minimum Distance Between Individual Bars
main reinforcing bars shall usually be not-less
than the greatest of the following:
1. The diameter of the bar if the diametera are
equal,
2. The diameter of the larger bar if the
diameters are unequaI, and
3. 5 mm more than the nominal maximum size
of coarse aggregate.
Greater horizontal distance than the minimum
specified in (a) should be provided wherever
possible. However when needle vibrators are
used the horizontal distance between bars of a
group may be reduced to two-thirds the
nominal maximum size of the coarse aggregate,
provided that sufficient space is left between
groups of bars to enable the vibrator to be
immersed.
Where there are two or more rows of bars, the
bars shall be vertically in line and the minimum
vertical distance between the bars shall be
15 mm, two-thirds the nominal maximum size
of aggregate or the maximum size of bars,
whichever is greater.
Maximum Distance Between Bars in Tension
Unless the calculation of crack widths shows that a
greater spacing is acceptable, thefollowing rules shall
be applied to flexural members in normal internal or
external conditions of exposure.
a) Beams - The horizontal distance between
parallel reinforcement bars, or groups, near the
tension face of a beam shall not be greater
than the value given in Table 15 depending on
the amount of redistribution carried out in
analysis and the characteristic strength of the
reinforcement.
Slabs
The horizontal distance between parallel main
reinforcement bars shall not be more than three
times thl effective depth of solid slab or
300 mm whichever is smaller.
The horizontal distance between parallel
reinforcement bars provided against
shrinkage and temperature shall not be more
than five times the effective depth of a solid
slab or 450 mm whichever is smaller.
Is This Answer Correct ? | 34 Yes | 7 No |
Answer / mitch
The minimum clear spacing between parallel bars in a layer shall be db(diameter of bar) but not less than 25mm. [see sec. 407.7 NSCP 2010 for Spacing limits for reinforcement.]
Is This Answer Correct ? | 11 Yes | 5 No |
Answer / manikanta p
Maximum use of steel in construction 50mm bar, and using of aggregate 20mm
Bar center to bar center minimum of spacing 50mm
Bar inner to inner 25mm minimum spacing required
Is This Answer Correct ? | 0 Yes | 2 No |
What is the procedure to calculate the compaction of sand?
what is meant by workebility of concrete?i have studied about it much but i can't clear about it.so plz give me a detail explanation in simple english or urdu ?
what is the degree of residential building stair case ?
wat is the proportion of M40?
how to do rate analysis for P.C.C 1:4:8 for 2.83cum(100cft)
2 Answers Unity Infraprojects,
what if i want to lap a 20mm dia and a 16mm dia together wat will be the lap length?? a) 1m b) 80mm
what is meant by velocity & gravity ?what is the difference between normal liquid flow & gravity liquid flow ?
what is the relation between pitch of steel and depth of slab?
state the main objectives of underpinning
please give me the rates of RCC(CUM), PCC(CUM), Brick Work(CUM), Tile Flooring, Saria Shuttering
how to find soil strength,and type of soil testing?
How many number of cement bags per running metre are required to cast pileof M-20 grade