Sir We have a REF relay connected to 10MVA(Y-Y) Transformer.on
External earth fault REF relay trips along with earth fault
relay.The REF relay has no complant as we tested relay.Why is
it happening?
Answers were Sorted based on User's Feedback
Answer / shariff
REF relay shold not operate otherthan its zone of operation
i.e 11kV REFR zone is from 11kV trf busings to 11kV CT
(incomer) and some times PT also if PT is before CT. It is
a mal function only and it can be any of the following.
1) Check the 11kV NCT wiring it may be loose/ got cut in
the NCT wiring box in the yard.
2) The 11kV incomer CT wiring may be loose/ got cut etc.
3) Check the 11kV PT primary resistance it may notbe equal.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.prakashchandra
The NCT is responsible..The ungrounded lead from The NCT may
be grounded.
| Is This Answer Correct ? | 1 Yes | 0 No |
Also may be due to 1 .reverse connection of NCT leads ( Unbalanced current of lines and NCT current add to each other ). 2. Low saturation point of NCT as Kv of bushing NCT is usually less than that of line CTs
| Is This Answer Correct ? | 0 Yes | 0 No |
Explain marx circuit.
Which of the following can be operated at higher frequencies ? -SCR -MOSFET -IGBT
what is meaning of AMF, WHY IS USING IN GENSET
Assuming that a dedicated neutral earthing transformer is provided for each GT generator, when the two generators are running in parallel, has consideration been given that the earth fault current from one generator stator winding be split between the two neutral earthing transformers? If so, what adverse impact will this have on the operation of the 59N and 27TN devices?
How to do the meggering for a cable.
What is the harm if we install primary side 11 KV VCB at a distance of one Km from the 11/3.3KV 12.5 MVA transformer through 11 KV cable.
what is creepage distance
WHAT IS LINIER MOTOR?
Hi everyone. Some Generators uses 3-Pole breakers with extra contactors for Neutral. Some uses 4-Pole. Why so? What is the idea behind this? Thanks in advance for the solution. Kr.
What is the criteria for selecting the voltage classes of an AC Induction Motor.The KW rating above/below which ht/lt selection is made may be provided in details.
Sir, I need a power supply at 380V. The supply I get in three phase is rated 415V. The total supply I have from the supply company is 70KW. Kindly inform if it is better to use a voltage stabiliser for this purpose or a transformer
what is KA rating and how can we choose switchgears on applications
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)