Sir We have a REF relay connected to 10MVA(Y-Y) Transformer.on
External earth fault REF relay trips along with earth fault
relay.The REF relay has no complant as we tested relay.Why is
it happening?
Answers were Sorted based on User's Feedback
Answer / shariff
REF relay shold not operate otherthan its zone of operation
i.e 11kV REFR zone is from 11kV trf busings to 11kV CT
(incomer) and some times PT also if PT is before CT. It is
a mal function only and it can be any of the following.
1) Check the 11kV NCT wiring it may be loose/ got cut in
the NCT wiring box in the yard.
2) The 11kV incomer CT wiring may be loose/ got cut etc.
3) Check the 11kV PT primary resistance it may notbe equal.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.prakashchandra
The NCT is responsible..The ungrounded lead from The NCT may
be grounded.
Is This Answer Correct ? | 1 Yes | 0 No |
Also may be due to 1 .reverse connection of NCT leads ( Unbalanced current of lines and NCT current add to each other ). 2. Low saturation point of NCT as Kv of bushing NCT is usually less than that of line CTs
Is This Answer Correct ? | 0 Yes | 0 No |
line vltage of three phase distribution transformer is 433v and phase voltage is 250v,but we required 230v for domestic distribution,then how we reduce phase voltage of transformer
How to take vector group test for Ynd11 transformer.
What is the difference between Floot charge and Trickle Charge.
what is the difference between a race around condition and toggling?
How we check vector group for a Dyn1 transformer?
what is the meaning of knee point in current transformer and how to calculate?
Should power factor be low or high?
what is the working principle of DC generator ?
What is fault.?
2 Answers AngloGold Ashanti, MNC,
Capacitors are used to ... -Reduce the bill of the farmer -Improve the PF
What descriptive information does the NEC require to be marked on all conductors?
Why high Voltages come in multiple of 11, like 11 KV, 33KV, 66 KV, 132 KV etc.