Sir We have a REF relay connected to 10MVA(Y-Y) Transformer.on
External earth fault REF relay trips along with earth fault
relay.The REF relay has no complant as we tested relay.Why is
it happening?
Answers were Sorted based on User's Feedback
Answer / shariff
REF relay shold not operate otherthan its zone of operation
i.e 11kV REFR zone is from 11kV trf busings to 11kV CT
(incomer) and some times PT also if PT is before CT. It is
a mal function only and it can be any of the following.
1) Check the 11kV NCT wiring it may be loose/ got cut in
the NCT wiring box in the yard.
2) The 11kV incomer CT wiring may be loose/ got cut etc.
3) Check the 11kV PT primary resistance it may notbe equal.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.prakashchandra
The NCT is responsible..The ungrounded lead from The NCT may
be grounded.
Is This Answer Correct ? | 1 Yes | 0 No |
Also may be due to 1 .reverse connection of NCT leads ( Unbalanced current of lines and NCT current add to each other ). 2. Low saturation point of NCT as Kv of bushing NCT is usually less than that of line CTs
Is This Answer Correct ? | 0 Yes | 0 No |
what is the function of mccb?
Why an ac systems are preferred over dc systems?
what is the difference between starter and control panel..?
What is voltage
What is ONAN/ONAF1/ONAF2 for transformer cooling
why two wires are wound alternately to each other in single phase wires?
What is the principle of residual protection?
The power factor of the fixed load is 0.8, now the p.f is varying from 0.8 to 0.5.
what is the size(sq.mm) of these conductors dog,rabbit,tiger,panther,mush,
what is KA rating and how can we choose switchgears on applications
who is ohm's and his law ?
why do we not use equivalent voltage source in negative sequence equivalent ckt.