In 63kva LT Distribution Box Why the outgoing of 63A kit kat
is connected to 200 A link disconnector? as the output of kit
kat is only 63 A?
Answer / k.prakashchandra
The link should be of at least twice the rating of fuses, as
otherwise you will have to replace links instead of fuses.
Is This Answer Correct ? | 1 Yes | 0 No |
Difference between RCCB, RCBO and ELMCB.
What are the tests to be done on circuit breaker?
Why 4 pole generator generates more power and 6 pole generates less power campare to 4 pole
2 Answers Julius Berger, Suzlon,
give 5 differences between relay and contactor
What are the types of Bus bar?
We have .ht motor which is 60Hz.we run on 50Hz.so that it's speed reduce but we had one prob.that motor winding temp increase up to 135 deg.we want reduce this temp.what to do?we arrange ext.cooling fan but not much effect.we want reduce this temp. Inhouse without affecting much.cost. also don't want reWINDING OF MOTOR?