what is the current rating of 2500 KVA,33KV/433v transformer
on secondary(LT) side
Answers were Sorted based on User's Feedback
Answer / srinivasa rao talasila
Primary current=2500000/1.732*33000
=43.74A
Secondary current is =2500000/1.732*433
=3333A
| Is This Answer Correct ? | 43 Yes | 4 No |
Answer / pillay
sec 433volts of a 3 phase 2500 KVA TXformer will be
2500,000 / 1.72 / 433 = 3356 amps.
| Is This Answer Correct ? | 13 Yes | 5 No |
Answer / raj
input power= output power => transformer do's.
depends on ur load they will design.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / gopal
HT CURRENT
I=LOAD/VOLTAGE
I=2500X1000/33*1000=75.75A
LT CURRENT
I=LOAD/1.732*433
I=2500*1000/1.732*433=3333A
OR USE SIMPLE FORMULA
1=LOAD X 1.4
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / l rc reddy
ht capacitors starting time line current load&unload
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / gnanendra
Hey.. It is very important to mention whether it is 1-phase or 3-phase.. See any text book.. If rating given means in that it will be definitely mentioned..
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / s bharath
p=1.732*v*i*0.8
2500=1.732*433*i*0.8
i=2500*1000/1.732*433*0.8
i=4.16kA
| Is This Answer Correct ? | 6 Yes | 8 No |
Answer / kaami
power in = power out
v*i = v*i=2500kVA
on input side
33kv*i=2500kv
i=2500/33=75.75amps
on output side
v*i=2500kva
433v*i=2500Kva
i=2500/433=5.7ka
so it is designed for 5.7KA on secondary side
| Is This Answer Correct ? | 19 Yes | 22 No |
Answer / rafeek
p=3^1/3*vicos$
=3^1/3*415*i*0.8
p = 575i
p=250*0.8=200kw
200*1000=575i
i=347.82
i=347.82*1.2=417.39
i-~=400amps
| Is This Answer Correct ? | 3 Yes | 9 No |
what is CRGO Transformers?
6 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd, TATA,
What is partial discharge in power cable?
WHY DOES NEUTRAL DO NOT CARRY EVEN THOUGH IT CARRIES RETURN CURRENT?
how the inductor will work on dc supply?whether it will work or not?
When dc supply is fed to rotor of the alternator how it work?
I am having a DG set.The 415 V from Generator is step up to 460 v and then the same is used for Induction furnace. before Step up, I am connecting LT load to my factory use. When Induction furnace is in service from DG, when i try to start a motor, the generator is tripped.Please tell me the reason.
What is TVSS Protection???
what is full form of dyn11( in transformer)
What are hrc fuses and where it is used?
What is the maximum load of 240mmsequre single core cable can carry?
what is LA CT PT panel?
3 Answers Dwarikesh Sugar Industries, NTPC,
what are the differant std sizes of cable trenches?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)