what is the current rating of 2500 KVA,33KV/433v transformer
on secondary(LT) side
Answers were Sorted based on User's Feedback
Answer / srinivasa rao talasila
Primary current=2500000/1.732*33000
=43.74A
Secondary current is =2500000/1.732*433
=3333A
| Is This Answer Correct ? | 43 Yes | 4 No |
Answer / pillay
sec 433volts of a 3 phase 2500 KVA TXformer will be
2500,000 / 1.72 / 433 = 3356 amps.
| Is This Answer Correct ? | 13 Yes | 5 No |
Answer / raj
input power= output power => transformer do's.
depends on ur load they will design.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / gopal
HT CURRENT
I=LOAD/VOLTAGE
I=2500X1000/33*1000=75.75A
LT CURRENT
I=LOAD/1.732*433
I=2500*1000/1.732*433=3333A
OR USE SIMPLE FORMULA
1=LOAD X 1.4
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / l rc reddy
ht capacitors starting time line current load&unload
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / gnanendra
Hey.. It is very important to mention whether it is 1-phase or 3-phase.. See any text book.. If rating given means in that it will be definitely mentioned..
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / s bharath
p=1.732*v*i*0.8
2500=1.732*433*i*0.8
i=2500*1000/1.732*433*0.8
i=4.16kA
| Is This Answer Correct ? | 6 Yes | 8 No |
Answer / kaami
power in = power out
v*i = v*i=2500kVA
on input side
33kv*i=2500kv
i=2500/33=75.75amps
on output side
v*i=2500kva
433v*i=2500Kva
i=2500/433=5.7ka
so it is designed for 5.7KA on secondary side
| Is This Answer Correct ? | 19 Yes | 22 No |
Answer / rafeek
p=3^1/3*vicos$
=3^1/3*415*i*0.8
p = 575i
p=250*0.8=200kw
200*1000=575i
i=347.82
i=347.82*1.2=417.39
i-~=400amps
| Is This Answer Correct ? | 3 Yes | 9 No |
What is Anemometer used to measure?
Currently what is the highest capacity (MVA) of SPPg generator available in the market?
what is a pf factor in generator.
tube light how its working.,?
What is difference between A.C & D.C Resistance ?
What is the power factor of a transformer at no load?
How to select earthing strip for 100kw induction motor ?
How can I calculate the Mega watts required to run a plant having many electric motors and other electrical components.
Why a dc generator gives result during two different condition,- 1)separately exited gen.- Eg=110 V, field current=0.25 A. 2) self exited gen.- Eg=30 V, field current=0.025 A.
How DC earth leakage currents can be reduced ?
what is the formular for the calculation of CT'S when installed as part of a electrical installation so the correct meter is used
Is Transol transformer oil comparable to nynas nytro libra?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)