what is the current rating of 2500 KVA,33KV/433v transformer
on secondary(LT) side
Answers were Sorted based on User's Feedback
Answer / srinivasa rao talasila
Primary current=2500000/1.732*33000
=43.74A
Secondary current is =2500000/1.732*433
=3333A
| Is This Answer Correct ? | 43 Yes | 4 No |
Answer / pillay
sec 433volts of a 3 phase 2500 KVA TXformer will be
2500,000 / 1.72 / 433 = 3356 amps.
| Is This Answer Correct ? | 13 Yes | 5 No |
Answer / raj
input power= output power => transformer do's.
depends on ur load they will design.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / gopal
HT CURRENT
I=LOAD/VOLTAGE
I=2500X1000/33*1000=75.75A
LT CURRENT
I=LOAD/1.732*433
I=2500*1000/1.732*433=3333A
OR USE SIMPLE FORMULA
1=LOAD X 1.4
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / l rc reddy
ht capacitors starting time line current load&unload
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / gnanendra
Hey.. It is very important to mention whether it is 1-phase or 3-phase.. See any text book.. If rating given means in that it will be definitely mentioned..
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / s bharath
p=1.732*v*i*0.8
2500=1.732*433*i*0.8
i=2500*1000/1.732*433*0.8
i=4.16kA
| Is This Answer Correct ? | 6 Yes | 8 No |
Answer / kaami
power in = power out
v*i = v*i=2500kVA
on input side
33kv*i=2500kv
i=2500/33=75.75amps
on output side
v*i=2500kva
433v*i=2500Kva
i=2500/433=5.7ka
so it is designed for 5.7KA on secondary side
| Is This Answer Correct ? | 19 Yes | 22 No |
Answer / rafeek
p=3^1/3*vicos$
=3^1/3*415*i*0.8
p = 575i
p=250*0.8=200kw
200*1000=575i
i=347.82
i=347.82*1.2=417.39
i-~=400amps
| Is This Answer Correct ? | 3 Yes | 9 No |
what must be the mf for a meter with the following conditions. line ct ratio-100/1 line pt ratio- 220kv/110v meter pt ratio- 3X63.5V meter CT ratio- -/1 A
Hello Can I use step up HV transformer 440/4160V as a step down? Thanks Evgeny
when turbine trips generator will becomes induction motor or synchronous motor?
What is the difference between LT CT & HT CT?Can we use indoor type transformer as an outdoor type or vice versa?
I have 1500/1A CT If i connect this CT in 6.6KV bus bar means what will be the voltage present in CT?
Why Drives are used to run AC motors?
explain different losses in a transformer.
how to give earthing in plain?
A wattmeter is marked 15 A/30A, 300V/600V and its scale is marked up to 4500 watt. When the meter is connected for 30A, 1600V, the pointer indicates 2000 watts. The actual power in the circuit in
What will hapen if we connect more capacitors than required for powerfactor control? Exactly what will be the effect on power system?
what is the meaning of knee point in current transformer and how to calculate?
Vaccum circuit breaker
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)