how to calculate short circuit calculation of the transformer
by usuing the percentage impedence?
formula needed.
Answer Posted / elangovan kp
Isc (Shot circuit Current ) = Full load current of Tranformer / Impedance(%)
Ex: for 1000 KVA, 11/0.415 KV Transformer , Percentage Impedance - 6% :
Full load current of LV side of Transformer = 1000 * 1000 / ( 415 * 1.732)
= (1391 / 6) * 100
= 23187 Amps.
| Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
where reactive power is used
Explain the difference between verilog task and verilog function?
Why let through energy not considered for ACB breaker while cable sizing?
hey guys i scored 910 on GRE and 67 on TOEFL respectively.I have an aggregate of about 74%in my B tech.For which colleges should i apply for an MS program in electrical engineering.I am looking for colleges in NJ,SC,NC,GEORGIA, NY. Please reply with a good response.....
ht side line to earth voltage
what is the relationship between current&voltage in practical purpose ?
Mention how NPN and PNP transistor works?
how to test power transformer.YNd11
What is s-domain and its significance?
can u describe the method used for protection of transmission line.
State superposition theorem?
is it necessary to earth the rmu before cutting off the transformer winding?if yes why?
Draw a circuit diagram in which if button is open we can use socket and bulb as a series test circit and if button is close than simple we can use socket as any load purpose.
How to confirm the Phase shifting Transformer VECTOR GROUP relation , as below ZNy11.45d10.45-ZNYy0.15d11.15
what will be the maximum winding temperature of 6.6kv HT motor 450kw, Full load current 49A. 50Hz Frequency.