how to improve IR value in HT motors?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
It is not possible to improve IR value as insulation can not
be injected.You can remove the water contents by heating the
coils by making full load current pass through ,using 3
phase dimmer-stat with rotor locked.
Is This Answer Correct ? | 15 Yes | 0 No |
Answer / prem
insulation resistance is measured using megger.if megger shows
meaurable value in tens or hundereds then just change the insulatin of lt motor to improve it.
Is This Answer Correct ? | 7 Yes | 4 No |
Answer / k.prakashchandra
With dimmer-stat (auto-transformer),it may not be possible
to get full load current in large motors .Then you have to
use strip heaters for heating the coils or DC supply (no
back emf)
Is This Answer Correct ? | 4 Yes | 1 No |
what is means of ALF,kPV(min),lexc(max)at Vk,Rct@75 degree centrigate ohm in current transformer name plate?
is it possible to run a dc motor on ac supply with good performance.....?
Which level of the Transformer oil got dielectric strengh? And why?
What is core CT & it's function?
In a 11kv/433v transformer,at the LT side ie 433 V side why do we need to put 3.5 core Cable upto Panel.The full load rated Amps is 666 at LV side.What value of current will flow through the Nuetral Conductor.Why can't we use 4Core Cable instea of that?
what is the diffrence between resistive load and capoasitive load.?
what is the speed of a turbine in an hydroelectric power station and how many poles does it have...?
Where I can get the sample question for post of Junior engineer electrical-II For RRB Bhubaneswar.
what is impedance in a transformer? how can i calculate it?
How to design inductive load for 3 phase 440v and maximum 5 amps for star or delta? Can we use a 15kW, 1450rpm motor for 15kW, 960rpm apllication?If yes.how......n.if thesame motor used what`s it`s sideeefect.
Why 268hp induction motor taking different current in three different phases? (In which two phase having same current and one having higher value compare to other 2 phases.)
Why do we need interlocking in a HT metering or Ring main unit switchgear?