how to improve IR value in HT motors?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
It is not possible to improve IR value as insulation can not
be injected.You can remove the water contents by heating the
coils by making full load current pass through ,using 3
phase dimmer-stat with rotor locked.
Is This Answer Correct ? | 15 Yes | 0 No |
Answer / prem
insulation resistance is measured using megger.if megger shows
meaurable value in tens or hundereds then just change the insulatin of lt motor to improve it.
Is This Answer Correct ? | 7 Yes | 4 No |
Answer / k.prakashchandra
With dimmer-stat (auto-transformer),it may not be possible
to get full load current in large motors .Then you have to
use strip heaters for heating the coils or DC supply (no
back emf)
Is This Answer Correct ? | 4 Yes | 1 No |
sometimes, eventhough the HV side of the transformer is opened there is a voltage in LV side .How is it possible?
if there is a voltage difference between neutral and earth when we operate any instrument for fraction of time then where is problem?
What is the meaning of Dyn11 of Transformer.
If 110 volts ac is mixed up ith 12 volts dc what will be the resultant voltage and what is the wave form?
Why the Motor takes High Current in Starting time?
What is resistance reading of earth copper rod with grid and without grid?
how to calculate the over current rating of 3phase motor
WHY WE CAN GENERATE POWER IN 3PHASE MODE ONLY NOT IN 4 OR 5 PHASE?
how much earthings are provided for 22KV HT Metering Kiosk
1 Answers GE, Gionee, Knight Frank, TATA, Vacmet,
at meter room 50 hrc switch installed,but there are not get earthing proper,so what happen?and 11kv transformer out put going in to hrc main 400a three nog each? so earthing is require for all switch? (some customer made earthing at there home.)
0 Answers Ebrahim Textile, Siemens,
How current is reduced in STAR connection?
I've heard that most of the substations are rated in multiples of 1.11 because of form factor.What is form factor?