Why transformer rating in KVA?
and Generator also?
Answers were Sorted based on User's Feedback
Answer / chvnraja
Any device is rated depending on losses of the machine. In a
transformer the losses are iron losses which depends on
voltage and copper losses which depends on current so there
are no losses which depend on power factor hence transformer
is rated in KVA
| Is This Answer Correct ? | 32 Yes | 0 No |
Answer / rahul
In a transformer Losses(I^2R-Iron and Copper Losses)depends
on voltage(Volts) and current(Amps).so the rating wshould
be in KVA
| Is This Answer Correct ? | 29 Yes | 5 No |
Answer / a.muthukumar, vacon
Cu loss of a transformer depends on current and iron loss on voltage. Hence, total transformer loss depends on volt-ampere (VA) and not on phase angle between voltage and current. It is independent of load power factor. That is why rating of transformer is in KVA and not in KW.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / nilamanineel@yahoo.com
but nobody did not say about alternator
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / deepak
this is because the KVA rating give active plus reactive
power components and the reactive power is associated with
losses of the machines. KW rating tells about the power
being transfered not the losses associated with the process.
| Is This Answer Correct ? | 3 Yes | 8 No |
Answer / aniket
as the is not known we cannot know the power factor so cant xpress in watts so in kva
| Is This Answer Correct ? | 5 Yes | 14 No |
why fan consume constant power even when we increase or decrease its circuit resistance through speed regulator???
where we use compound motors in real time and why?
If the damper winding on the rotor of a synchronous motor is removed after starting what will happen?
Why capacitor is blow when I am starting motor ?
Why we generate power at multiple of 11 i.e 11kv,33kv etc.
9 Answers DTV Solutions, Havells, TCS,
What is function of inverter? and who it's operate & what are controlling devices are used?
what is vibration?
how tto ingress mw in turbine explain.procedure ?
if field breaker of generator is closed prior to its rated speed on a power generating unit. what will be the effect on generator, unit transformer and starting transformer.
plz tell me Motor IP formula
A wattmeter is marked 15 A/30A, 300V/600V and its scale is marked up to 4500 watt. When the meter is connected for 30A, 1600V, the pointer indicates 2000 watts. The actual power in the circuit in
In LT cables 3.5 core cable are available that means 3 core and .5 for neutral Why .5 for neutral and is there any reason for that please suggest thanks and regards pavan kumar
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)