Why transformer rating in KVA?
and Generator also?
Answers were Sorted based on User's Feedback
Answer / chvnraja
Any device is rated depending on losses of the machine. In a
transformer the losses are iron losses which depends on
voltage and copper losses which depends on current so there
are no losses which depend on power factor hence transformer
is rated in KVA
Is This Answer Correct ? | 32 Yes | 0 No |
Answer / rahul
In a transformer Losses(I^2R-Iron and Copper Losses)depends
on voltage(Volts) and current(Amps).so the rating wshould
be in KVA
Is This Answer Correct ? | 29 Yes | 5 No |
Answer / a.muthukumar, vacon
Cu loss of a transformer depends on current and iron loss on voltage. Hence, total transformer loss depends on volt-ampere (VA) and not on phase angle between voltage and current. It is independent of load power factor. That is why rating of transformer is in KVA and not in KW.
Is This Answer Correct ? | 17 Yes | 1 No |
Answer / nilamanineel@yahoo.com
but nobody did not say about alternator
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / deepak
this is because the KVA rating give active plus reactive
power components and the reactive power is associated with
losses of the machines. KW rating tells about the power
being transfered not the losses associated with the process.
Is This Answer Correct ? | 3 Yes | 8 No |
Answer / aniket
as the is not known we cannot know the power factor so cant xpress in watts so in kva
Is This Answer Correct ? | 5 Yes | 14 No |
what is the range of using dol starter & star delta starter.
What are the two segments of nyquist contour.
In Swinburne's Test on D.C.machines, why the efficiency is more when the machine runs as generator than when it runs as motor???
6 Answers College School Exams Tests, GE, MVR, Practical Viva Questions,
why DC current not used in Transformer action?
17 Answers Engineers India Limited,
When a square wave is applied to primary of a transformer then what will be output wave form of secondary ?
15 Answers Bhel, Sail, Sterling Telecom, TCS,
what is basically a pulse transformer?
What are the types of windings present in the ceiling fan? What winding will be effective first when we started the fan?What are the resistance and inductance ratios comparatively at the initial speed and full speed of the fan?
How to convert 2 phase to 3 phase electricpower in induction moter?
Can the same motor be operated in both direction ?
What are the types of feedback oscillators?
what is the function and use of cable differential protection relay?
how can we select the rating of Load break switch that is connected to the primary protection of 200 kva 11kv/415v distribution transformer?? step by step calculated answr pls...thnk.u