Why transformer rating in KVA?
and Generator also?
Answers were Sorted based on User's Feedback
Answer / chvnraja
Any device is rated depending on losses of the machine. In a
transformer the losses are iron losses which depends on
voltage and copper losses which depends on current so there
are no losses which depend on power factor hence transformer
is rated in KVA
| Is This Answer Correct ? | 32 Yes | 0 No |
Answer / rahul
In a transformer Losses(I^2R-Iron and Copper Losses)depends
on voltage(Volts) and current(Amps).so the rating wshould
be in KVA
| Is This Answer Correct ? | 29 Yes | 5 No |
Answer / a.muthukumar, vacon
Cu loss of a transformer depends on current and iron loss on voltage. Hence, total transformer loss depends on volt-ampere (VA) and not on phase angle between voltage and current. It is independent of load power factor. That is why rating of transformer is in KVA and not in KW.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / nilamanineel@yahoo.com
but nobody did not say about alternator
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / deepak
this is because the KVA rating give active plus reactive
power components and the reactive power is associated with
losses of the machines. KW rating tells about the power
being transfered not the losses associated with the process.
| Is This Answer Correct ? | 3 Yes | 8 No |
Answer / aniket
as the is not known we cannot know the power factor so cant xpress in watts so in kva
| Is This Answer Correct ? | 5 Yes | 14 No |
Efficient electrical earthing in hard rock area
What happens when ac supply is given as excitation voltage instead of dc supply
What will be cross section area of copper conductor for carry 2000 amps & 2500 amps....sq.mm.?/
What are the basic component of a cro?
how we calculate the short circuit capacity of the busbar in LV & HT?
can a generator with 15AH specified battery for starting can be connected to a battery of greater capacity?
which turbine has high thermal efficiency a)open gas turbine b)close gas turbine
how calculation to be done of cable size/o.h. conductor size of 11kv h.t.for the load of 2175 kw
why any Elelctricity board insist not to change the buren of their metering CTs or PTs for metering purpose? as a example elect. board not accepted that any customer change their metering CT or PT core burden from 5VA to 15VA.. why?
what is the practical definition for voltage
what is the advantage of NiCd battery over Lead acid battery?
what is the different types of cable lugs?
2 Answers Green Power, Kum Yang,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)