What is the suitable rating of MCB for 1.5 Ton A.C and why?
1Ton= how many amperes?
Answers were Sorted based on User's Feedback
Answer / manoj kumar sahoo
20 amps is the suitable rating of MCB for 1.5 Ton A.C &
because in starting time it takes 1.5 times more current of
the full load current .1 Ton=09 amps.
| Is This Answer Correct ? | 122 Yes | 32 No |
Answer / smruti
20amp mcb is the perfect rating mcb for 1.5 ton ac due to 1.5 times of stating current.
| Is This Answer Correct ? | 44 Yes | 13 No |
Answer / vishvajeet
Because of compressor at the start current may be more than
5In , but once atrted it will take In only , os 'C' type
mcb only should be refer , now current depends upon the
watt rating so uo to 2.5kw 16 amp MCB can be used but if it
is more than 2.5 kw to 3.5 kw go with 20amp mcb only
| Is This Answer Correct ? | 34 Yes | 13 No |
Answer / ananthanarayanan
For 1.5 ton 1743 w power consumption AC, went with 16 A type C MCB.
Digital domestic House Electric meter showed around 8 Amp current for AC only.
1.5 times 8 is around 12
Hence 16 A is best for power consumption around 1743 W.
| Is This Answer Correct ? | 20 Yes | 7 No |
Answer / gautam lasgotra
For 1.5 ton ac you should use at least a 32 ampere dp mcb.
| Is This Answer Correct ? | 3 Yes | 26 No |
what is magnetizing current test in power transformer
how we explain parallel paths armature winding?
what type circuit breaker is suitable for connecting 1000A load VCb,Mccb?
If 100 KAV USP dedicated earth got disconnect / Cut. What will happen at load.
Explain few advantages of electric traction system?
To test Transformer we give HT side 440V to see wheather that it is producing 17.6V on LT to verify Voltage ratio is correct or not but when we give the 440V voltage to LT side then what will happen to HT voltage ?
what is linear motor?
Difference of induction motor & servo motor ??
0 Answers Macpower CNC Machines,
what type of cables exsisting in the world and how many types
Is necessary Protection CT, CLASS - 5P10 fitted at Incomer side of main Breaker ? Why ?
how to determine the cable size...pls explain me with the formula taking particular load....does the factors like impedance & short circuit rating influence the cable size, if so how....
In between UPS out going changer over switch and ups raising main input, both side cable gland producing heat but the cable doesn't get heat,Why?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)