What is the suitable rating of MCB for 1.5 Ton A.C and why?
1Ton= how many amperes?
Answers were Sorted based on User's Feedback
Answer / manoj kumar sahoo
20 amps is the suitable rating of MCB for 1.5 Ton A.C &
because in starting time it takes 1.5 times more current of
the full load current .1 Ton=09 amps.
| Is This Answer Correct ? | 122 Yes | 32 No |
Answer / smruti
20amp mcb is the perfect rating mcb for 1.5 ton ac due to 1.5 times of stating current.
| Is This Answer Correct ? | 44 Yes | 13 No |
Answer / vishvajeet
Because of compressor at the start current may be more than
5In , but once atrted it will take In only , os 'C' type
mcb only should be refer , now current depends upon the
watt rating so uo to 2.5kw 16 amp MCB can be used but if it
is more than 2.5 kw to 3.5 kw go with 20amp mcb only
| Is This Answer Correct ? | 34 Yes | 13 No |
Answer / ananthanarayanan
For 1.5 ton 1743 w power consumption AC, went with 16 A type C MCB.
Digital domestic House Electric meter showed around 8 Amp current for AC only.
1.5 times 8 is around 12
Hence 16 A is best for power consumption around 1743 W.
| Is This Answer Correct ? | 20 Yes | 7 No |
Answer / gautam lasgotra
For 1.5 ton ac you should use at least a 32 ampere dp mcb.
| Is This Answer Correct ? | 3 Yes | 26 No |
in ACB breaker requireding 3200Amps. buscoupler getting OFF mode and again it reset and getting normal position give me a required answer?
Capacitor bank require for 1000amp load
2 Answers Biodeal, Pharmaceutical,
Briefly define and explain the following different types of Pulse Amplitude Modulation (PAM) with some examples. i) 2-PAM ii) 4-PAM iii) 8-PAM iv) 16-PAM v) Quadrature Amplitude Modulation (QAM)
What is the use of conservater, bucchos relay, breather in a transformer?
8 Answers Bosch, Wipro, Zadco,
What is stacking factor? What is its approximate value?
What is the difference between the transmission line and distribution line?
what is the difference between changer, converter and transformer?
is there any phase difference occurs while primary and secondary side mutual induction occurs?
how can i increase the excitation on full load running engine??
Can Dy11 and Dy1 vector group transformers be paralleled?
can we use 400w coke instead of 250w choke in 250w fittings
what is difference between differential protection and distance protection and how we calculate the sloop?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)