why we grounding the neutral of a transformer?
Answers were Sorted based on User's Feedback
Answer / alok das
To grounding the neutral of a transformer becease this time
neutral is works as earthing. And the earthing safety they
transformer by any kinds of electrical falts. over load
current & lighting.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / bhavesh patel
grounding of neutral is because of whenever there is fault in equipment, the excessive current flow through in it and it will ground through neutral wire
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / simon peter
In distribution transformer the secondary side is always in star connection i,.e a neutal piont is drawn. Neutal wire & the core of x-mer is connected to earthing bcs if there is enormous load variation the overall load will b on phase wires hense x-mer might blow off due to increase in the value of hysteresis & eddy losses........
| Is This Answer Correct ? | 2 Yes | 2 No |
How to find the maximum load, that can be supplied by a transformer.....
2 Diesel Generators 900KVA connected to the bus bar for essential load as an alternative for power taken from 11/440V 3KVA Transformer supplying this bus bar. my question here is in the event of power failure on 11KV side can I feed the power to 11 KV bus by using the same transformer as reverse feed, what will be the inrush current???
what is is the potential diffrence between two phase ?
What are the types of instrument transformer?
we can stepdown the voltage from 230/12v ,and we use the voltage for various electronics components why can't we step up the voltage from 12/230v if we can shall we use the voltage for domestic single phase supply
what the effect will occur if we increase the airgap in induction motor
1.What is captive power plant? 2.What is national grid?Give brief idea.
why we get 2 differnet values for power factor in 2 watt meter method in 3 phase
auto reclosing scheme for radial ehv feeder is to be implemented or not?
why we have to particulary use ACB for below ratings,even available of MCB,MCCB with that range ?
2 Answers QRG Health City, Siemens,
If a line which is drawing approximatly 2100amps what should be earthing streep size(using galwanize streep)?
What are the advantages of the three-phase motor over single phase motor?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)