What Should be the rating of transformer used in 33KV
substation?
Answers were Sorted based on User's Feedback
Answer / rahul m
In a 33/11 Kv substation 2.15 MVA to 10 MVA power
transformers will be used and in 132/33 KV Substations 25
MVA and above will be used
Is This Answer Correct ? | 26 Yes | 3 No |
Answer / prashanth
IN A 33/11 KV SUBSTATION UPTO 8MVA POWER TRANSFORMERS WILL
BE USED AND IN 132/33 KV SUBSTATION ABOVE 8MVA TO 31.5MVA
POWER TRANSFORMER WILL BE USED
Is This Answer Correct ? | 11 Yes | 2 No |
Hi If connecting a temp generator 670KVA .415kv with step up Tx .415/11kv. I am given Generator impedances Z1 Z2 Z0 to 100MVA base. Do I need to work out the generator fault current by using these impedances i.e gen rating / impedance. Then use this as my source impedance for the calculations that follow.
what is the difference between synchronous motor and induction motor?
what is the difference betwteen overcurrent and short circuit fault?
what is mean by PID & Principal of working
why 3 phase motors are preferable over single phase motors ?
WHY DISEL GENRATOR SET SHUT DOWN IN OVER LOAD CONDITIONS
What is trickle charging system?
Difference between EDO and MDO breakers?
What is the difference between short circuit and overload currents?
Advantages/Disadvantages of earthing of neutral bus on MSB instead of separate neutral earthing for transformer/DG sets feeding to MSB
what role neutral plays in electrical circuit? If neutral is not there what will be the effect
what is earth-fault?when it occurs? to check where it occurs what type of test should we do?