Answer / rahul m
In a 33/11 Kv substation 2.15 MVA to 10 MVA power
transformers will be used and in 132/33 KV Substations 25
MVA and above will be used
Is This Answer Correct ? | 26 Yes | 3 No |
Answer / prashanth
IN A 33/11 KV SUBSTATION UPTO 8MVA POWER TRANSFORMERS WILL
BE USED AND IN 132/33 KV SUBSTATION ABOVE 8MVA TO 31.5MVA
POWER TRANSFORMER WILL BE USED
Is This Answer Correct ? | 11 Yes | 2 No |
What is a soft start?
either water sensor or flow meter,how we observe the water level, f any other equipment are in market ?
i need list of swg(standard wire guage) or area of conductor v/s current carrying capacity of conductor copper & alluminium...
what is inductance function?
When a single pase capacitor run motor- run on 230vac and Case(1)run with 8 Mfd 250 vac.capacitor , Case( 2) run with 8 Mfd 400vac capacitor. What is difference between both case regarding power ,efficiency etc?
is dc shunt moter oprate on ac? if no why? if yes how?
8 Answers IOCL, JJJ, Power Grid,
How to connected to energy meter, pt, ct, ammeter, voltmeter and selector switch.
what is impedence in transformer
HOW CAN YOU CALCULATE PRACTICAL EFFICIENCY OF A ASYNCHRONOUS INDUCTIONMOTOR OF 7.5KW,& MOTOR IS RUNNING WITH AVOLTAGE OF 410 VOLTS,& TAKING CURENT OF 13 AMPS
they transformer oil leakeage to beather tank and top parts . they protection relayes was not operated.what is the oil leakeage problem.
how to calculate the over current rating of 3phase motor
In our domestic single phase line if you don't have a ground connection (earthing)how will you separately use earth in a specific power supply board.