Transformer capacity is 250 KVA
Primary current = 250000/1.732x11000= 13.12 Amps
Short circuit current ( 6 times primary current )
total current would comes -----90 amps
Size of the cable --- 3c X 35/ 50 sq.mm 11 kv HT XLPE
cable is required for primary
Secondary side current -----333.35 amps
cable size is 3.5 c X 300 sq.mm AYFY cable is required
Is This Answer Correct ? | 23 Yes | 15 No |
IS it a 250 KVA or 2500 KVA transformer? any way you must
know the operating current first before determining the
cable size. if 250 kva than 250000 / 11000 / 1,732 = 13.12
amps the cable should be able to withstand 11000 volts and
carry 13.12 amps.
Is This Answer Correct ? | 14 Yes | 9 No |