WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS
TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AND ITS CABLE IS
4CX50SQMM ,NOW ITS GETTING ABNORMAL HEATUP IN CABLE,PLZ
TELL WHY ITS HEAT-UP?(CABLE LENGTH IS 15 METERS ONLY)

Answers were Sorted based on User's Feedback



WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / k.prakashchandra

Normally 70 sq mm Al cable or 50 sq mm copper cable is used
for 100 A current.As the length is only 15 m it may not
matter.If ,only the cable ends are getting heated
,connections may be checked.If entire length is getting
heated, voltage drop across the cables is to be measured.If
it is more than 2 % ,the cables have to be replaced for poor
quality of conductor material and insufficient sectional
area due to it.

Is This Answer Correct ?    10 Yes 0 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / maprayil

It would be unfair for anyone to answer your question with
the given inputs. Please also mention the network voltage
(operating voltage) and type of cable, i.e., Al or Cu.

Is This Answer Correct ?    2 Yes 0 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / mohammad a.monem salama abu se

THE RERATING FACTOR MAY BE VERY LOW BECAUSE OF EXISTING
GROUP OF CABLES IN THE SAME TRENCH OR ANY OTHER REASON .YOU
HAVE TO KNOW THE CONDITIONS OF THR AREA WHERE THE CABLE IS
LAID.

Is This Answer Correct ?    1 Yes 0 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / manohar

If motor is connected in Y/D connection, then the cable size
is used OK, Check the both motor & panel side terminal
connection is loose . After this if you found cable heating
then check the voltage,current& POWER FACTOR. If necessary
put 25KVAR Capacitor Bank at motor side.

Is This Answer Correct ?    1 Yes 0 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / adeleke

Your question shows that you have measured the current. If
this is correct at 100A and your cable is copper conductor,
there is no reason why the cable should be hot or even warm
no matter the installation method.The two possibilities are
the ambient temperature, the grouping of the cables or the
quality of the copper conductor used.

Is This Answer Correct ?    2 Yes 1 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / laxmi

if you are used 50sq.mm alu.cable it may not sufficient to
carry the 100 amps current,for alu. cable 1A for 1Sq.mm is
a safe factor load.if your cable is copper it is enough to
carry your load.as per your information your cable length
is not a problem.

Is This Answer Correct ?    1 Yes 1 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / sreekar

we must use above 70Sqmm Al cable for best results.

Is This Answer Correct ?    3 Yes 4 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / santosh kumar

Always write capacity of motor in HP. your motor efficiancy
is 70%. with 100% efficiancy should be 145A with 380V.
please check the voltage & Current with load on motor
terminal. and use cable (in Sqmm) half of the running
current. I think your cable voltage drop should be 15 to
39V as per loadind.

Is This Answer Correct ?    2 Yes 3 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / k.prakashchandra

Further, if the armour is earthed at both ends ,there is
likelihood of cable getting heated.

Is This Answer Correct ?    1 Yes 2 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / michael

you use 80mm^2 wire, motor has starting current. 1.25 of full load,

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

no of rotrs poles in salient pole synchronous machine

3 Answers  


will the power consumption remains the same when speed of the fan cnanges??if so y??

2 Answers  


Metal covered multiconductor cables shall employ a marker tape located within the cable running for its complete length in lieu of cable surface marking. Is it true or false?

0 Answers  


Name two low frequency oscillators?

0 Answers  


What is the d/f between DOL & star delta starter & automatic star delta starter?

23 Answers   ACC, Dalkia, Engineering, Indeco, NINL, Novotel, RMH Control Systems, Wipro,






Earth has zero potential then what would be the neutral potential ?

0 Answers   JLL,


Zone of protection and tripping scheme of arc protection relay.

0 Answers   KSEB, L&T, Siemens,


how we calculate full load current of A.C & D.C Motors?

1 Answers  


What are methods to avoid the inrush current at the time of starting of power transformer ?

8 Answers   Wipro,


Hello everyone, somebody knows what is a "surplice power" ? The hole phrase is: "This rating is appropriate for a generator set paralleled with an infinite bus e.g. a national electrical supply network or grid where the generator set is run at 100% load, 24 hours a day, 365 days a year and any surplice power is exported into the grid" Thanks in advance.

0 Answers  


what is an S.C.R. and how do they work?

4 Answers   GE,


why in the three pin plug all 3 pins are cutted ?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)