Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS
TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AND ITS CABLE IS
4CX50SQMM ,NOW ITS GETTING ABNORMAL HEATUP IN CABLE,PLZ
TELL WHY ITS HEAT-UP?(CABLE LENGTH IS 15 METERS ONLY)

Answers were Sorted based on User's Feedback



WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / k.prakashchandra

Normally 70 sq mm Al cable or 50 sq mm copper cable is used
for 100 A current.As the length is only 15 m it may not
matter.If ,only the cable ends are getting heated
,connections may be checked.If entire length is getting
heated, voltage drop across the cables is to be measured.If
it is more than 2 % ,the cables have to be replaced for poor
quality of conductor material and insufficient sectional
area due to it.

Is This Answer Correct ?    10 Yes 0 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / maprayil

It would be unfair for anyone to answer your question with
the given inputs. Please also mention the network voltage
(operating voltage) and type of cable, i.e., Al or Cu.

Is This Answer Correct ?    2 Yes 0 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / mohammad a.monem salama abu se

THE RERATING FACTOR MAY BE VERY LOW BECAUSE OF EXISTING
GROUP OF CABLES IN THE SAME TRENCH OR ANY OTHER REASON .YOU
HAVE TO KNOW THE CONDITIONS OF THR AREA WHERE THE CABLE IS
LAID.

Is This Answer Correct ?    1 Yes 0 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / manohar

If motor is connected in Y/D connection, then the cable size
is used OK, Check the both motor & panel side terminal
connection is loose . After this if you found cable heating
then check the voltage,current& POWER FACTOR. If necessary
put 25KVAR Capacitor Bank at motor side.

Is This Answer Correct ?    1 Yes 0 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / adeleke

Your question shows that you have measured the current. If
this is correct at 100A and your cable is copper conductor,
there is no reason why the cable should be hot or even warm
no matter the installation method.The two possibilities are
the ambient temperature, the grouping of the cables or the
quality of the copper conductor used.

Is This Answer Correct ?    2 Yes 1 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / laxmi

if you are used 50sq.mm alu.cable it may not sufficient to
carry the 100 amps current,for alu. cable 1A for 1Sq.mm is
a safe factor load.if your cable is copper it is enough to
carry your load.as per your information your cable length
is not a problem.

Is This Answer Correct ?    1 Yes 1 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / sreekar

we must use above 70Sqmm Al cable for best results.

Is This Answer Correct ?    3 Yes 4 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / santosh kumar

Always write capacity of motor in HP. your motor efficiancy
is 70%. with 100% efficiancy should be 145A with 380V.
please check the voltage & Current with load on motor
terminal. and use cable (in Sqmm) half of the running
current. I think your cable voltage drop should be 15 to
39V as per loadind.

Is This Answer Correct ?    2 Yes 3 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / k.prakashchandra

Further, if the armour is earthed at both ends ,there is
likelihood of cable getting heated.

Is This Answer Correct ?    1 Yes 2 No

WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AN..

Answer / michael

you use 80mm^2 wire, motor has starting current. 1.25 of full load,

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

what is meant by unity power factor?unity means one why dont call 2,3,4......?

6 Answers  


what will be happen if we apply D.C supply to the transformer

14 Answers   CCBPL,


What is the need of black rock stones under the transformer yard?

5 Answers   TNEB Tamil Nadu Electricity Board,


Why phase sequence ryb called colours.

1 Answers   MS Life, NTPC,


Suppose a 3 phase, 2 pole, 440V induction motor is driving a flywheel of 600mm diameter, 150kg mass. By using v-belt and pulley, the speed is increased to 4500 RPM. What will be the effect on motor current?

0 Answers  


what is vcb & working principal

4 Answers   JLL,


What is plc and how to do preventive maintenance

1 Answers  


SMPS (Switch Mode Power Supply) unit is denoted by KW or KVA?

6 Answers  


Define closed loop control system.

0 Answers  


How to do maintenance of transformer feeder.

0 Answers   KSEB, L&T, Siemens,


What will be the fault current of any system when its generation is 10% of BASE generation( FUll Load )?Will is 10% or the same as full base calculation?

0 Answers  


wat is the advantage of increse in frequency?how the powersupply range decreses as the frequency increses?like in america,it uses 110 ac and 60 hz?

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)