what is advantage of providing taping on HT side?
Answers were Sorted based on User's Feedback
Answer / e.subash
Dear sir plz check your transformer OLTC Technical
specification and simply i tell difference
Transformer ratio = 3.3 KV/ 33 KV
Current = 785 A / 75A
if i provided OLTC in Low voltage side means
1) What is the OLTC size
2) Quanity of the material and Size of Contact points and
other things (Copper)
3)Transitent surges Compare When fault will happen
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / erarun
As per standard we have to maintain stable secondary voltage means load for uninterrupted power supply. To maintain secondary voltage constant we have to change the tap to higher value when supply (Primary) voltage is low.So this is first reason.
And second reason is that always LT winding put near to the core to provide lower insulation material rather than HT winding insulation.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / abhishek goyal
Major factor is insulation of winding of transformer because
at the LV side it will nearer to the core or inside section
and HV is wound at the outer section of core or upper on LV
winding side. If we put tape changer at LV it is very
difficult to get there winding at outer portion (it will
effect on maintenance or manf point of view).
Other factor is if we change voltage at LV SIDE it should be
change very little as per requirement SO we will connect
tape changer at HV side for constant or stable voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rajan
Onely HT side tape volage high current low copper size less BUT LV side current high voltage low copper size ingrese
| Is This Answer Correct ? | 0 Yes | 0 No |
Why do you have to use Protecion relay with the function MTB ( Mechanical Trip Button ) for electrical system.
what is humming AC solenoid
Cb closed condition if there is a tcs fail whether cb will trip or not
what is the working principle of soft-starter & how it diff. from VFD ?????????
how much percentage set in transformer diffrencial relay
Why rating of transmission line in kv not in kva
Why is the earth fault relay connected to the Yellow Phase?
Sir pl provide 5 year sample paper for post junior engineer(electrical).I have currently applied for junior engineer (electrical) on RRB Ajmer
why no load characteristics of generator also called as occ
A synchronous machines has higher capacity for (1) Leading power factor (2) Lagging power factor (3) Does not depend upon the power factor of machine (4) None of the above
Three phase alternators are connected in star connection why?
for 500mw power production how many range of transformer set in unit please reply if three transformer use .
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)