what is advantage of providing taping on HT side?
Answers were Sorted based on User's Feedback
Answer / e.subash
Dear sir plz check your transformer OLTC Technical
specification and simply i tell difference
Transformer ratio = 3.3 KV/ 33 KV
Current = 785 A / 75A
if i provided OLTC in Low voltage side means
1) What is the OLTC size
2) Quanity of the material and Size of Contact points and
other things (Copper)
3)Transitent surges Compare When fault will happen
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / erarun
As per standard we have to maintain stable secondary voltage means load for uninterrupted power supply. To maintain secondary voltage constant we have to change the tap to higher value when supply (Primary) voltage is low.So this is first reason.
And second reason is that always LT winding put near to the core to provide lower insulation material rather than HT winding insulation.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / abhishek goyal
Major factor is insulation of winding of transformer because
at the LV side it will nearer to the core or inside section
and HV is wound at the outer section of core or upper on LV
winding side. If we put tape changer at LV it is very
difficult to get there winding at outer portion (it will
effect on maintenance or manf point of view).
Other factor is if we change voltage at LV SIDE it should be
change very little as per requirement SO we will connect
tape changer at HV side for constant or stable voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rajan
Onely HT side tape volage high current low copper size less BUT LV side current high voltage low copper size ingrese
| Is This Answer Correct ? | 0 Yes | 0 No |
For two systems transmitting the same amount of real power, the system with the lower power factor will have higher circulating currents due to energy that returns to the source from energy storage in the load.???
what is field flash
What happens if we run alternator on under frequency?
How to calculate the electrical load for a standard telecom BTS shelter and choose the DG set capacity for the same load?
Whats the minimum value for I.R. that can be allowed for HT & LT alternators for operation?
what is power and what is watts detailed description and formulas
what is mean by NPS (Negative phase sequence)fault? what is the difference between EFR & OCR faults?
0 Answers TNEB Tamil Nadu Electricity Board, Vestas,
how to convert kw in to unit
how can we find a burden of potential transformer? what does it effects? how can we calculate rated load of it?
WHICH IS BETTER( FOR POWER SAVING)- ON LINE OR OFF LINE UPS ?
3 Answers Punjab National Bank,
what is FS cable?? Difference between FS and FRLS??
what is the use of surge suppresser in 33 KV incoming panel. where it must be installed,inseries with incoming cable surge suppresser must be at incoming of the breaker are outgoing of the breaker
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)