Answer / raj
secondary should not be kept open... your question is wrong.
either it should be connected to measuring device or must be
shorted and grounded properly in order to avoid blast.
| Is This Answer Correct ? | 19 Yes | 0 No |
Answer / siddu
it will cause dangerously high secondary voltage and wen it s energized it should be loaded.
| Is This Answer Correct ? | 5 Yes | 0 No |
The secondary of ct is never open. It is always in a closed
circuit as connected to another coil that produces magnetic
force to cause deflection (The more current passing thru
the primary is the more magnitude of force to cause
deflection to the needle) to the needle used in reading
amperes such as ammeter thus serving the purpose of ct, to
be able to measure current.
| Is This Answer Correct ? | 11 Yes | 8 No |
Answer / rushi913@gmail.com
resultant voltge will increse and possibility of damaging
the winding will be occure which will be dangerous for man
who are operating this instrument
| Is This Answer Correct ? | 6 Yes | 5 No |
What are the different types of dams?
what is the problem of generator over voltage.?except automatic voltage regulator card
after parallaing two generators current is shooting up in both the generators.for ex: load is 400 kw..after paralling and load sharing current in running gen is approx 900 amps and incoming is 750 amps which is too high when trying toshift the load current in incoming gen is coming more than 1300 amps and both getting tripped and making blackout..
LT cable fault chaecking equipment and to find out the distance at what distence it failure . Name and where it is available?
0 Answers Himatsingka Seide Ltd,
A system absorbs 100 k J of heat and the increase in its internal energy is 100 kJ; the work done is
What is application of MCB & How it works
in soft starter system for 375 KW 3 ph induction motor for multi stage vertical pump, two thyristers failed causing shorting of thyrister. the motor winding failed while starting.What is the cause and what is the effect in above case
There is any especial requirement for motor to drive through with VFD?
in alternator what is use of AVR ? how AVR is operating either AC or DC?
what are the differance between neutral and earthing?
how we have to calculate the short circuit current for 33/11kv 2mva, 7.5% Z, Transformer primary side breaker and secondary side breaker short circuit current for both sides?.
What is ferrite affects and what is disadvantage of ferrite affects.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)