how to check IR values in alternator winding?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Isolate all phase windings at both ends and measure IR of
each phase to body and between windings
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / subash
A. Purpose and Theory
The IR test measures the resistance of the electrical
insulation between the copper conductors and the core of
the stator or the rotor. Ideally this resistance is
infinite, since after all, the purpose of the insulation is
to block current flow between the copper and the core. In
practice, the IR is not infinitely high. Usually, the lower
the insulation resistance, the more likely it is that there
is a problem with the insulation.
PI is a variation of the IR test. PI is the ratio of the IR
measured after voltage has been applied for 10 minutes
(R10) to the IR measured after one minute (R1), i.e.:
PI = R10/R1
A low PI indicates that a winding may be contaminated with
oil, dirt, insects, etc. or soaked with water. In the test,
a relatively high DC voltage is applied between the winding
copper and the stator or rotor core (usually via the
machine frame). The current flowing in the circuit is then
measured
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / nithin
Insulation resistance of alternator is checked using a megger and before measuring it the connections to the protective devices like CT,PT and also the connection to the AVR to be disconnected. Then the star connection of the winding to be disconnected ,then we can check IR value
| Is This Answer Correct ? | 0 Yes | 0 No |
how to calculate energy meter multipling factor by ct & pt raitio
what is the reason for choosing DYn11 in transformer, why not DYn12 or something else
If 3-Ph motor of same rating connected in Delta & Star for same load one by one then which connection take more current in running (not in starting)for full load.(eg 8.5 KW,3-Ph 400 V)
Explain the Term in CT Name Plate – Class: 5P10
Sir We have a REF relay connected to 10MVA(Y-Y) Transformer.on External earth fault REF relay trips along with earth fault relay.The REF relay has no complant as we tested relay.Why is it happening?
How we do the maintenance of Servo motor, even we cant open it?
Generally the incandescent lamps in bathrooms fuse due to high voltage at night.What is the simple solution of this problem?
kVA rating of open delta connected transformer is _____% kVA rating of delta/delta connection A 50 B 70.7 C 57.7 D 75.7
Explain Analog and Digital signals?
what is the difference between arc and spark
what will happen reduce the transformer voltage from 415v to 406v, is it save the energy,? are this methodis good to reduce the energy.?
how could we calculate the no of outgoings from a 800 watt distribution board
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)