What happen when ct secondary are open circuited? why same
thing is not happen in ordinary transformer?
Answers were Sorted based on User's Feedback
Answer / nithi
when SEC of the CT open circuited,
1.high-voltage buil-up in the sec side
2.core saturation-over heat-result in fire(if
prolonged).
these things will not happen in ordinary
transformer.because,
PRIMARY CURRENT IS REFLECTION OF SECONDARY
CURRENT.SO,WHEN THERE IS NO CURRENT IN sec SIDE,ONLY NO-
LOAD CURRENT WILL FLOW IN PY WINDING.BUT IN CASE OF CT,PY
CURRENT IS INDEPENDENT.SO,IF SEC OPENED,NO DE-MAGNETISING
EFFECT &FORCED TO OVERFLUXING CONDITION.
| Is This Answer Correct ? | 22 Yes | 0 No |
Answer / pritam upadhyay nit p
when secondary is open there ic no flux due to secondary
current to oppose flux due to primary so due to high flux
there is very high voltage induced on secondary side which
causes sparking and damage of core due to high flux demsity.
in case of power transformer flux is constant whtheer
primary open or not so there is no such case as in ct..
| Is This Answer Correct ? | 1 Yes | 0 No |
If secondary of CT is opened and as we know that primary
always flow the current and by transformaton action
secondary must flow the current but in our case secondary
is opened hence Extra high voltage is induced in terminals
of secondary which can be fatal.
In case of ordinary transformer if secondary is open
primary flows only no load current hence secondary voltage
is only rated secondary votage which is not as danger as in
the case of CT.
| Is This Answer Correct ? | 1 Yes | 0 No |
define one ampere?
What is CBCT ,why and whereit is used?
what is phase to phase to phase to ground fault
For 7.5HP motor 2880rpm 415VAC Connected with Pressurisation Fan we used Star Delta Startor why not we use DOL startor
draw the full wave and half wave circuit of 3 phase system and inverter circuit used in ups
what is power and what is watts detailed description and formulas
25 kva 3 phase dg how many current will take per phase , plssssssss reply me
During the main stator winding insulation testing (phase to ground)of 11kv alternator (Lerysomer) i found 0 and resistance with multimeter and found 20 killo ohm while the power cables are connected both end (Generator & VCB). In VCB PT (Potential transformer) are connected. Please any body explain that method of insulation is correct or not? also describe of PT connections
how is working d.c amps meter?how to connect the dc ammeter inthe circuite?
Why is water motor not taking the pressure? what is the problem?
what types battery chargers are there?wanted with details.
Which one is correct mVA or MVA. Whether both the units are same for the transformer
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)