what is puling in n pulling out in flame scanner system?
Answer / bala
Flame Scnner Basic function- viewing flame in furnace
It has provided in order to avoid unwante boiler trip
Pull in / pull out manual set value from 0 - 100 %
pull in always higher than pull out eg- 40 % & pull out 20 %
when initial flame exceed above 40 % it will consider as
flame
when flame drop drop from 40 - 20 it will consider as flame
when drop below 20 % it will take as no flame signal
the o/p contact flame / noflame will be taken for boiler
safty operation
| Is This Answer Correct ? | 6 Yes | 0 No |
where Pirani gauges are uesd in case of pressure measurement?
what type of cables are used for f&G systems and detectors, what is the standard colour?
WHAT IS THIS INSTRUMENTATION?
what is compensation? temprature & pressure
can i get any detail of interview question asked for instrumentation,plc,scada ,dcs..............
How to calculate flow of air bubbler type level transmiter According hight and density
2 Answers Qatar Petroleums, RKS,
what does 5/2 solinoid valve means?
Rtd sensor how to calibrate
In my company plc based winders are operated. one day there was a data transmission failure alarm shown on pc. as per sir instruction we have reset master plc but winders were not triped and alarm gone. so what master plc do?
Exothermic reaction./ endothermic reaction
What is rang ability?
pls send me the 10 years technical question papers of NTPC AND BHEL
15 Answers Bhel, NTPC, ONGC, UCE,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)