i work as a technician at a private company.. i used to take
amp reading for certain appliances such as air con.. the
problem is when i clamp the neutral, wire there is a current
reading.. from my understanding for single phase system
neutral should not have current unless if the circuit is not
complete.. yet the air con still work
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
You may not expect current in neutral of a 3phase
appliance. But there will be current in neutral of a 1
phase appliance while working.,
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / pillay
your understanding is wrong or if not
incomplete.
In any single phase circuit the neutral
is the return path
for the circuit. That means the current that
flows into the phase comes out through the neutral
Even in 3 PH balanced load you will see the
same individual ph current in the neutral but
you will see no current in the main neutral,
cos at the neutral bar the individual neutral
current had balanced up through the other phases.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / snk
yes your thinking good and by law should not be flow when
open circuit.but air con working and neutral floe is the
return of current.you make your question in tow parts then it
will be help full.
| Is This Answer Correct ? | 0 Yes | 1 No |
what is mean by flux
What id difference between power and energy?
why the star delta motors burn out frequently
difference between over current and over load protection?
How much earthing require for h.t.22 k.v. cable in coming side & out going & 22 lighting arrest or,22 k.v.D.o. & A.B. switch.
what is direct dischage of power transformer
why transformer is rated in KVA ?
plz explain TSM and PSM.with example suppose ct ratio is 4000/5 and tsm is .15 and plug is at 3.75 if fault current is 8000A.so how i find relay oprating time.
2 Answers College School Exams Tests, ME,
what is proper capacitor placement? How to evaluate capacitor size?
I have a relay contact rated at 220v dc which is supplied with a 24vdc from the panel,for it to trip the dampers(24vdc).What if the application of the relay changes so that it should work at its rated 220vdc then will it work at 24vdc supply given or any other consideration needs to be taken .....
what is meant by vector group in transformers? wy we r using that?
why transformer rating in kva
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)