oil sample dielectric test gives the insulation rupture
voltage at 26 kv. is this transformer safe to be operated .
The working voltage is 11 kv
Answers were Sorted based on User's Feedback
Answer / sms
AS PER IS:6792 , Oil Electric break down voltage( BDV) at
room temp using 2.5 mm gap should be Min 30 KV .
Accordingly don't take risk and carry out oil filteration
as early as possible to avoid any break down.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / k.prakashchandra
40 KV is the minimum value required. You need not panic.
Measure the BDV again after 15 days. If there is drop ,oil
filtering is to be done at the earliest
| Is This Answer Correct ? | 1 Yes | 1 No |
3.The slip of an IM UNDER FL condition is about.....
In case of any eventuality, who is your next of kin?
2 Answers Edison, Foster Wheeler, GE, GE Energy, HP, Infosys, Koch Industries, Roper Industries, Siemens,
Please define ampere?
why weight is put on pulley?
how much distance is required for earth pit to earth pit in substation???
what is the name for a meter/tester to measure the paint quality in electrical panel or wall?
What will hapen if we run generator below 47.6hz frequency?
What is the name and type of power transformer oil?
definition of transformer
Should transformer earthing pit, to be connect to earthing mat in Substation
what is the function of switch gear ?
WHICH TYPE OF TRANSFORMER IS USED IN POWER TRANSMISSION BASED ON TRANSFORMER CONNECTION ON PRIMARY AND SECONDARY SIDE
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)