Consider a level troll.
i am getting a correct value in 4mA and 20mA.
the value in the middle(30 to 60%)is disturbed and i am not
getting the appropriate value.
what is the solution to normalize the level and to get the
correct value..
Answers were Sorted based on User's Feedback
Answer / joe mccabe
a) calc the hyteresis and reset the 4-20 to it, accepting
the deviation in the middle
b) test the amount of deviation @ 4ma,8ma,12ma, 16ma,&20ma
and see if slope is repeatable, write program correction
for slope
c) Your instrument has a hardware issue, do the right thing
and replace it.
| Is This Answer Correct ? | 6 Yes | 1 No |
Just Simply Calibrate the transmitter With Different ranges
check for
0% should get 4mA
25% should get 8mA
50% should get 12mA
75% should get 16mA
100% should get 20mA
take reading from Increasing and decreasing Reading. And
According to which plz Set ZERO or SPAN.
| Is This Answer Correct ? | 1 Yes | 8 No |
what is XV and KV valves?
pressure switch range 0 to 2bar.i have to install from ground level to 5 meters height.what is the formula the to increse the range ? and every 1 meter how much pressure should be add ?
in yokogawa prosef rd safety PLC how to data send frome local SCS to other SCS and other FCS
What is the procedure of calibration of Load cell?
Manipulation of dead wt. tester double piston type.
Hi at present i m wrking with tire industry as a manager having gud ctc. Nw I am selected for 1 of the best chemical industry but my ctc is lower than current n also i hv 2 compromize vit post as post is also lower. I hv 6 yrs of exp in various type of industry. Should i join chemical industry as there ar lot of gud instrument than tire? Financialy i can manage 4 more 2 yrs. Bt during wrking vit tire industry i found there is very less instrument n feel that opportunity is less. Pl ans quickly. I have less time to decide.
where cascade loop use ?
For a diafhram 1.5 d =kn(p-p0) D4 Where d in deflection in inch k=constant n=no of capdule (P-P0)=Applied pressure in psi D In active dia at capsule. -1.5 d=k to p d being constant -1.5
0 Answers L&T, Shiv Tech Marine Control,
In my company plc based winders are operated. one day there was a data transmission failure alarm shown on pc. as per sir instruction we have reset master plc but winders were not triped and alarm gone. so what master plc do?
how many pulses are required by a ac induction servo motor of 4 poles with 50 Hz frequency to rotate by 1 degree?
why we go for pcbs
why gray colour is choosing to all instrument panel.why not choosing other colour?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)