Consider a level troll.
i am getting a correct value in 4mA and 20mA.
the value in the middle(30 to 60%)is disturbed and i am not
getting the appropriate value.
what is the solution to normalize the level and to get the
correct value..
Answers were Sorted based on User's Feedback
Answer / joe mccabe
a) calc the hyteresis and reset the 4-20 to it, accepting
the deviation in the middle
b) test the amount of deviation @ 4ma,8ma,12ma, 16ma,&20ma
and see if slope is repeatable, write program correction
for slope
c) Your instrument has a hardware issue, do the right thing
and replace it.
Is This Answer Correct ? | 6 Yes | 1 No |
Just Simply Calibrate the transmitter With Different ranges
check for
0% should get 4mA
25% should get 8mA
50% should get 12mA
75% should get 16mA
100% should get 20mA
take reading from Increasing and decreasing Reading. And
According to which plz Set ZERO or SPAN.
Is This Answer Correct ? | 1 Yes | 8 No |
Why humidity limit is 30 to 55 % for raw material storage?
TRANSDUSER MOSTLY CONVERT WHICH ENERGY INTO ENERGY ?
what is droop mode n frequency mode in wood ward governor?
please explain about actuator action? direct action & return action ?
Explain operation of Haskel pump.
can any one help me to get bel probational engineers sample question papers. I have applied for it.
Conversions
where do you give the 4-20 ma i/p in a MIL control valve?
How many types of sensors are used in instrumentation & what are names
Explain the working of an electronic level troll.
what's meanning of 1250KVA and how to calculate with Volttage and Current. answer give with example.
what is hart communicater? can u give brief explanation about this issue?