ALF--accuracy limit factor(ratio of nominal over current to the rated current)
KPV--knee point voltage(secondary voltage must be less than KVP so that ct accuracy will not hampered)
KPV=k.Is(Rct+Zs) where Rct=resistance of secondary winding at 75 c
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / m.esakkiraja
1. ALF - Accuracy Limit Factor
It is the ratio of Instrument limit primary current to the Rated primary current.
2. KPV- Knee point Voltage
It is defined as a point where 10% increase in the Secondary Voltage causes an increase in the Secondary Current by 50%.
3. Iexc- Excitation current
A transformer exciting current is the current or amperes required to energize the core.
4. Rct @75°C - Resistance of Secondary winding on CT at 75°C.
| Is This Answer Correct ? | 1 Yes | 0 No |
Why is water motor not taking the pressure? what is the problem?
What is magneto on a gas generator. how it functions. its out put is d.c or a.c. how it can be checked for correct functioning
i have dry type transformers can you help me that how many tests i can do to know the performence of transformer and also please tell me about the BDV test and Insulation resistance test in oil cooled transformers
What are merits & De-merits of State-Space Method? What is series programming, parallel programming, general programming & direct programming ? And, difference between these programmings Techniques ?
What is the major difference between cnc and plc. why cant we use plc instead of cnc
As a good company employee, can you report your supervisor to the company management if he or she is going against the company interest in his or her actions?
why motors are rated in HP?
How ElCB tripping if Neutral touch with ground
power 148kw i need exat cable size in 148 kw in 3phase what size of cable can i used.
What is quadrantal symmetry?
fog produced due to?
why in an electrical lab a bulb connected to supply goes off slowly when the main supply is switched off?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)