Ah*voltage /1000=stored energy in Kwh = back up time in
hours * load in KW. Here instead of load, rating of
inverter is given in Kva. So with load at 65% 0f inverter
rating or at 65% of stored energy, the above formula nearly
holds good
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / vivek
As per industrial thumb rule we need 12V/130AH battery to
have 1 hour backup for 1 KVA UPS. Therefore 130 is
iindicates AH which always constant for 1 KVA.
| Is This Answer Correct ? | 1 Yes | 2 No |
Sir, why generating power plant operating at above 0.9 lag? detail explaination?
What is the equivalent circuit of a transformer and its vector diagram?
how to identyfy cable sizes?
why the rating of a transformer in kva not in kw.
given data are load current & power factor cable core size? plz any one update the calculation formula
What is ZCT? it operating principle and how is work with RCCB (residual current circuit breaker)?
why transformer rating in KVA or MVA instead of KW n MW??
how will be power factor while using the resistive load and Capacitive load?
what is the difference b/w low voltage motors & medium voltage motors
What is the meaning of insulation leavel LI 75 AC 28 About scott transformer spcification
what is surge??
Why does The speed of motor used in elevator remain constant irrespective of load??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)