UPS battery Back time = no.of Batteries * Ah of the Battery /
output KVA * 130 ? what is the 130 means ? can any one help?
because all are using this formula how its came 130?
Answers were Sorted based on User's Feedback
Ah*voltage /1000=stored energy in Kwh = back up time in
hours * load in KW. Here instead of load, rating of
inverter is given in Kva. So with load at 65% 0f inverter
rating or at 65% of stored energy, the above formula nearly
holds good
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / vivek
As per industrial thumb rule we need 12V/130AH battery to
have 1 hour backup for 1 KVA UPS. Therefore 130 is
iindicates AH which always constant for 1 KVA.
| Is This Answer Correct ? | 1 Yes | 2 No |
in Telecom DC system-why positive +ve is made earthed.and - ve is fed to load.
How to reduce the static electricity producing in solvent room? By P.D.Patil BioCon
what is the value of current and voltage that our body can resist ?
I HAVE A 50A MCCB AS PER DESIGN LINE WIRE CONNECT UPWORD SIDE AND LOAD IS CONNECTED TO DOWNWARD SIDE TO THE MCCB.IF NOW ANY ONE CHANGE SUPPLY & LOAD(WISEVERSA) WHAT HAPPENS ? DOES MCCB OPERATION OR WORKING FUNCTION NORMAL IF YES THAN WHY THERE ARE MARKED LINE & LOAD ON MCCB.
Why there is not any reactive power in DC although it causes magnetic field.
PLease anyone can tell me CTUM-15 specification?
HOW many type of Circut Breaker in the world used in 400 kv substation?
-What shall be short circuit current of LV switchgear for a 1000 kva, 11.415kv, 3 phase tranformer with 5% reactance.
how to calculte capacitor range for single phase induction motors??pls tel
for what purpose the star point is done in ct
Short circuit voltage of a transformer mainly depend on A ohmic resistance of primary B ohmic resistance of secondary C magnitude of leakage flux D cross sectional area of core
What will be the impact on motor performance if a LT motor is rewound with changed motor winding data as given below:- Original winding data: total 04 wires = 02 wires of 17 SWG + 02 wires of 16.5 SWG. Changed Winding data: total 03 wires of 15.5 SWG wire size Motor rating: 160KW, 740RPM, 415V, ID FAN application. Normal Running Current = 95% of FL Current.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)