How can we calculate ngr resistance for a generator and
Transformer ?
What type of transformer requires ngr ?
Answer Posted / pavan
The value of the NGR to be inserted in the cicuit can be
calculated by the simple formula
R = V / (√3 * I)
Where V is the System Line voltage in Volts
I is the value of the fault current to be limited
In general practice the fault current is limited to the
full load rating of the largest equipment available in the
system.
Is This Answer Correct ? | 6 Yes | 5 No |
Post New Answer View All Answers
Is it true online ups having bypass mode if it is true then why we called ups because it is interrupting power when goes in bypass mode
What is the differentional relay...what is the work of this in power Tx. how it is works..
Why compensation is necessary in feedback control system?
in control scheme dc logic wiring commonly using negative loop,what is the reason?if we use positive looping what will happen?
how to interlock 3 nos MCCBs using under voltage coil. please provide me circuit diagram?
what is solkor relay and which condition it will act?
for 4 MVA , 33K.V/6.6K.V transformer. secondary side the connected load is 3000H.P. What is the rating of capacitor bank to be insttaled.
Why the earth to phase voltage is high 250 compare to other two phases
What is the count of hvdc transmission lines in india?
i karmveer bharti persuing b.tech . plz send me syllabus and name of reference books. for preparation of section eng.
If we have use two power cable for incomer, that time how many use cbct for earth leakage protection? 1 or 2 if 1 way? If 2 way?
how give earthing conection to household equipment?
Enlists the applications of sampled data systems?
how can we save enegry by using VFD for Resiprocating Air compressor which is having more unloading running hours
difference between a diode and thyristor?