What is the voltage violating limit to be considered for
load flow study? What is acceptable deviation limit
according to relevant standards?
Answer / omar aziz
Mostly standards (IEEE , ANSI) recommend 5% however, in
practical situations where a sound judgment can be made you
can strech it upto 10 - 15% at the load bus depending on
your min. voltage allowed by the motors/ other equipment.
Motors can usually start at around 80% rated voltage ,
however other electronic equipment such as UPSs are very
sensitive to voltage variations.
Consider the load before selecting this threshold otherwise
stick to 5%
Is This Answer Correct ? | 1 Yes | 0 No |
what is the advantage of pwm pulse compare to squarewave pulse.
at meter room 50 hrc switch installed,but there are not get earthing proper,so what happen?and 11kv transformer out put going in to hrc main 400a three nog each? so earthing is require for all switch? (some customer made earthing at there home.)
0 Answers Ebrahim Textile, Siemens,
How many 2 ton window A/c can runs on a 125 KVA generator?
i want bhel placement paper for electrical if anybody having pl send to my id kavitha867@myway.com immediately
3) How earthing is done? How it measured? Write the method for earthing? How the earth resistance is kept low?
sir i am pradeep singh from electrical branch and i want to place in software industry(tcs)but i dont know much about programmig languages like c c++.so how can i get a placement in software industry?
how we can decide that what value of ht line will come to any commercial building? (ans except According to the building load)
is the power of a single phase induction motor(Fans) is constant under varying speeds?
how to calculate current carrying capacity in power cable?
a transformer runs by electro-induction principle like all motors.then why dosen't it rotate just like any other motor
What is phase cross over frequency?
What should be the amps for a MV fuses for transformer 630kVA 20(10)/0.4 kV