What is mean by earthed & unearthed cable? Voltage grade of
1.9/3.3 kV(E), 3.3/3.3 kV(UE), 3.8/6.6 kV(E)what it
indicates??
Answers were Sorted based on User's Feedback
Answer / ganeesh jain
There are earthed and unearthed cables for earthed and unearthed systems respectively.
Here, 1.9/3.3 kV = Uo/U = Phase to Earth Volt / Phase to Phase
1.9 X 1.732 = 3.3
Previously our systems were of small ratings and hence the short circuit faults were less and therefore lesser insulations were required for conductor. Whereas in advancement of time in modular system, huge fault currents are present and hence the insulation level on cables.
In earthed systems, Phase to earth voltage is 1.732 times the phase to phase voltage, where as in unearthed systems, phase to earth voltage can be equal to phase to phase voltage.
Therefore in earthed system ,stress on conductor to armour is 1.732 times lesser than the stress on conductor to conductor and hence lesser insulation is required between conductor and armour while in unearthed systems, since Ph-Earth voltage can be same as that of Ph-Ph voltage therefore the stress between conductor and armour will be more and hence the insulation.
Therefore manufacturers have designed 3 insulation classes for cables as per system design.
Insulation Class:
1. 100% : For solidly earthed systems, or on any system where the protective device will clear earth faults within 1 minute.
2. 133% : For systems where the protective device is expected to clear earth faults within 1 hour, and is typically specified for high impedance earthed or unearthed systems.
3. 173% : For systems where the time to clear an earth fault is indefinite. This is typically recommended for unearthed or resonant earthed systems.
In simple logic the 11 KV earthed cable is suitable for use in 6.6 KV unearthed system. The process of manufacture of cable is same. The size of cable will depend on current rating and voltage level.
Voltage Grade (Uo/U) where Uo is Phase to Earth Voltage & U is Phase to Phase Voltage.
Earthed system has insulation grade of KV / 1.75 x KV.
For Earthed System (Uo/U): 1.9/3.3 kV, 3.8/6.6 kV, 6.35/11 kV, 12.7/22 kV and 19/33 kV.
Unearthed system has insulation grade of KV / KV.
For Unearthed System (Uo/U): 3.3/3.3 kV and 11/11 kV.
3 phase 3 wire system has normally Unearthed grade cables and 3 phase 4 wire systems can be used earthed grade cables, insulation used is less, and cost is less.
Is This Answer Correct ? | 9 Yes | 0 No |
The metal sheath is earthed or unearthed. 1.9/3.3 and
3.8/6.6 are phase/ line voltages and are 3 core
cables.3.3/3.3 KV means 2 core cable for single phase
supply ,as neutral is present earthing is not necessary.UE
means unearthed E means earthed
Is This Answer Correct ? | 14 Yes | 9 No |
what will be the effect if we increase the excitation of a alternator??
How do you select a cable size(Cu&Al) for a particular load
10 Answers Adhunik, BPCL Bharat Petroleum, Hiecon, TATA,
How to check the thermocouple is correctly connected to cable for K type? (i,e positive pole is connected to non magnetic conductor and negative pole is connected to magnetic conductor)
hi this is hema can anyone mail me previous years questions for the APPSC-A.E.E (in electrical stream.) ......thank u.
what will happen if the connections of protection ct reverse? will it burn the ct?
What is a compensator?
How generating electric power export to grid from the generating station ?
FOR 3 PHASE DISTRIBUTION,WHY WE USE ONLY THE VOLTAGE LEVEL OF 440 VOLTS
AVR
Why CBCT rating is 50/1A
explain the f=np/120 this equ.how to come 120
3 Answers Jayaswal Neco Industries,
star delta starter single line digram