i have one temperature TX in my loop check time once i was
remove elament temp gose maximum then i am conect corectly
but still now temp showing maximum what can i do this
problem?
Answers were Sorted based on User's Feedback
Answer / rkb
your xmtr is in the state of Hi alarm latched. and it can
reset once you switch off the power supply(24VDC).
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / santosh nanavati
U have to reset the transmitter by switching off & on its
power or u have to go through transmitter configuration and
remove its maximum temp. hold condition in open signal
cable condition defined in it.
Is This Answer Correct ? | 1 Yes | 0 No |