how we can check that any motor is faulty may be single
phase or three phase?

Answers were Sorted based on User's Feedback



how we can check that any motor is faulty may be single phase or three phase?..

Answer / p.senthil kumar

1.you can check the ohmic value by using multi meter in
between r-y,y-b,r-b of motor windings & it must be the same
ohmic value for fine motor winding.
2.also check insullation value of each winding R,Y,B with
reference to earth.in that megger meter must shown infinite
value for fine motor winding condition.if it is shown zero
motor stator winding is defective.
3.for single phase check for connectivity of winding in
between running & starting winding.also check for a faulty
capacitor.

Is This Answer Correct ?    13 Yes 0 No

how we can check that any motor is faulty may be single phase or three phase?..

Answer / monika hassan

sigle phase or three phase the test protocols are same as
per IS325. By conducting priliminary test like IR value
measurement, resistance measurement, No-load run test etc.
all these tests ensures the healthy ness of the machine.

Is This Answer Correct ?    12 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is difference between short ckt and overload?

6 Answers   Siemens,


why the secondary current transformer cannot left open

1 Answers  


how to calculate bus-bar sizes? (copper bus-bars)

2 Answers  


Can we loop AC neutral wire with DC neutral wire?

5 Answers   ABB,


as per BIS supply voltage in India is ......

9 Answers  






define displacement & magnitude ?

0 Answers  


advantage of motor design on higher power factor . normally motors are designed for .8 power factor. what is advantage of designing at .88 power factor

0 Answers  


can you give main difference between ELCB And RCCB?

38 Answers   MCB Bank, Reliance, Wipro,


what is differentila pilot supervision in the incomer control panel in the power station?

0 Answers  


we have two generators different capacity on 15 MW and other 6MW at 11 KV , 15 MW gen. bus short level current 40KA,and 6MW short level current 25KA,, length of cable 100MTR between 6 MW from 15MW gen. for bus coupling . kindly tell any one can we use both NGR OR one NGR from any GEN. BOTH NGR has diff. rating. Tariq pakistan

0 Answers   RYK Mills,


how can i determine the KVA/MVA rating of transformer precisely?? is there any standard test?????

0 Answers  


where rlc series ckt used?

0 Answers   ABB,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)