how we can check that any motor is faulty may be single
phase or three phase?
Answers were Sorted based on User's Feedback
Answer / p.senthil kumar
1.you can check the ohmic value by using multi meter in
between r-y,y-b,r-b of motor windings & it must be the same
ohmic value for fine motor winding.
2.also check insullation value of each winding R,Y,B with
reference to earth.in that megger meter must shown infinite
value for fine motor winding condition.if it is shown zero
motor stator winding is defective.
3.for single phase check for connectivity of winding in
between running & starting winding.also check for a faulty
capacitor.
Is This Answer Correct ? | 13 Yes | 0 No |
Answer / monika hassan
sigle phase or three phase the test protocols are same as
per IS325. By conducting priliminary test like IR value
measurement, resistance measurement, No-load run test etc.
all these tests ensures the healthy ness of the machine.
Is This Answer Correct ? | 12 Yes | 0 No |
what is difference between short ckt and overload?
why the secondary current transformer cannot left open
how to calculate bus-bar sizes? (copper bus-bars)
Can we loop AC neutral wire with DC neutral wire?
as per BIS supply voltage in India is ......
define displacement & magnitude ?
advantage of motor design on higher power factor . normally motors are designed for .8 power factor. what is advantage of designing at .88 power factor
can you give main difference between ELCB And RCCB?
38 Answers MCB Bank, Reliance, Wipro,
what is differentila pilot supervision in the incomer control panel in the power station?
we have two generators different capacity on 15 MW and other 6MW at 11 KV , 15 MW gen. bus short level current 40KA,and 6MW short level current 25KA,, length of cable 100MTR between 6 MW from 15MW gen. for bus coupling . kindly tell any one can we use both NGR OR one NGR from any GEN. BOTH NGR has diff. rating. Tariq pakistan
how can i determine the KVA/MVA rating of transformer precisely?? is there any standard test?????
where rlc series ckt used?