what is the knee point voltage in current transformer
Answers were Sorted based on User's Feedback
Answer / satendra
On increasing the voltage the current will also be increase (as the res. is constant)in turn flux will also be increase.
But after the saturation point on increasing the voltage the current will go infinite momently. This point is called KNEE-POINT. After the knee point there are a more chances to get the coil as a permanent magnet. So we never perform the test upto knee-point.
satendra.svnit@gmail.com
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / chetan sharma
10 % increase in voltage gives you 50 % increase in
excitation current is called knee point voltage.
To measure this first demagnetise the CT and apply
voltage gradually from secondary keeping primary
winding open circuited. while doing this above
phenomeneo will be obsesrved.
Is This Answer Correct ? | 1 Yes | 1 No |
I have a question, I visit 01 site and face a problem, there is 2.5 ton Air Con working, when air con compressor is running at that time rectifier voltages are increasing upto 290-295 v and rectifier is giving main high alarm (rectifier is APC single phase, before starting compressor rectifier voltages was 230v. when air con is going off rectifier voltages are decreasing smoothly at its actual voltages 230v. Load on Genset phases is this: Red-13.5 amp AC (Air Con load), Yellow-1.7 amp AC (BTS lights etc.) and Blew-4 amp AC (telecom system load), Genset phase to phase and neutral to phase voltages are also ok. These are 10 sites having same system and same rectifier APC brand at every site 02 genset are working but the problem is same at all these 10 sites. What will be the reason behind???
deisel generators all elcetical calculation formule's
725KW Three DG set Synchronised but DG no-1 power showing 750KW DG n0-2 power showing 500KW DG no-03 showing 500KW. DG is Shynchronised but why this different power showing?
what is bus pt and what is the function of it
1 Ton is equal to how many watts?
For 415v,3phase,22kw rating of motor how to calculate MCCB rating
Recently we had experienced following problem All RCCB breakers (connected to the load as well as spares) connected to various UPS systems at various floors at a high rise building tripped during a power break down and upon starting up of generator.This Generator is recently inducted into the installation. Can any one explain the reason behind this tripping. Regards Viswanathan
How to connect frequency meter in metering circuit?(single phase and three phase frequency meter)
If 440 V supply has given at the secondary winding of transformer at that time if we apply 11 KV at primery then what will happen???????
if one potential missing in energy meter , how much % slow the energy meter?
How to decrease or increase the range of voltmeter? can an ammeter be used to measure voltage? can a wattmeter used as voltmeter and ammeter?
why ht motors are star connected?