Answer / siva
The restriction of current flow from the Earth Faults which
are Caused outside the Circuit of the Protected Equipment is
called Restricted Earth fault relay.
It is act as defense from nuisance!
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / jrk
EARTH FAULT CAUSED WITH IN ZONE IS CALLED RESTRICTED EARTH
FAULT.
| Is This Answer Correct ? | 2 Yes | 0 No |
REFP is mainly used for high speed tripping on star connected earthed secondary winding of power transformer
The relay does not operate for fault beyond the protected zone i.e neutral of the transformer.
Fault occurring near neutral is having small current becoz of small voltage which results in low fault current. To attend this fault the relay must be too sensitive to operate .To operate, the relay is set for the earth fault current of the order 15%of the rated winding current which protects restricted portion of the winding.
| Is This Answer Correct ? | 1 Yes | 0 No |
I want to do a mini project. Now I'm studying in 6th semis tor EEE Engineering.
Just a silly question but just to make my curious mind bac to normal - Why was not 67 and 67N relays built into a single relay as i have noticed that the R,Y,B CT wiring end up into the 67 relay while the common of the R,Y,B CT wiring end up into the 67N relay. Then it was better if a single relay was manufactured just like the distance relay (21). Another question i would like to ask is - how do we know where the 67 and 67 N relay has to be placed.why is it not placed at the transformer bay? In the substaion that i am working -i have noticed that it is placed between a breaker and a common double bus bar and this line bay is connected to another substation at a remote place which is furthur connected to a load. B U S______CT for 67 & 67N ______Breaker _____ remot s/s. B A R
what determins the amount of voltage produced by a voltaic cell?
difference bewteen reverse current and alternating current
what is the relation between the leading pf and supply voltage?
why DOL starter is use in induction motor as it is not reduce the starting torque
Do you know the faults occurs generally in motors and how to rectify them?
Why is our voltage always seems to be 3.3Kv,11Kv,66Kvetc.. why not 40Kv,39Kv,65Kv???
Dear sir,how should i set the relay in star delta starter..say ex i am having 4ohp motor,,wht should be the relay setting...?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
How much should be the load percentage for 15kva Inverter and Iinut & I output load with Calculations
What is the Resposiblity of Electrical Utility Engineer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)