what is resticted earth fault protection ? how did it
protect & work in power transformer
Answers were Sorted based on User's Feedback
Answer / siva
The restriction of current flow from the Earth Faults which
are Caused outside the Circuit of the Protected Equipment is
called Restricted Earth fault relay.
It is act as defense from nuisance!
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / jrk
EARTH FAULT CAUSED WITH IN ZONE IS CALLED RESTRICTED EARTH
FAULT.
Is This Answer Correct ? | 2 Yes | 0 No |
REFP is mainly used for high speed tripping on star connected earthed secondary winding of power transformer
The relay does not operate for fault beyond the protected zone i.e neutral of the transformer.
Fault occurring near neutral is having small current becoz of small voltage which results in low fault current. To attend this fault the relay must be too sensitive to operate .To operate, the relay is set for the earth fault current of the order 15%of the rated winding current which protects restricted portion of the winding.
Is This Answer Correct ? | 1 Yes | 0 No |
How much pf maintan in dg set in 6o% load,when Dg runnig Neutaal Earthing removed what happen.
BSNL TTA EXAM QUESTION
why capacitor using the induction motor?
WTA used cb?
When batteries are connected in series the voltage increases but the current remains unchanged, how can this be? When you consider ohm's law. i.e. If voltage increases, current increases, providing resistance remains the same.
what could be the possible reasons for copper cable to have low insualation?
what is positive , negative & zero equivalent system resistance
what will happen to give a dc supply in transformers?
which bridge is used to measure frequency?
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SIZES??
14 Answers Dubai Group, Saudi Delta Groups, Savitha Electricals,
write down the formula of cable size in RM if current is 50Amp.