Answer / rajdeepghosh8
current chopping in CB is the incident of arc current
interruption before normal current zero is reached.If This
current is enough to deliver a voltage which is greater than
restriking voltage then the arc will continue again. But
gradually the current falls and certainly the voltage also
reduces and finally fall down the restriking voltage and
ultimately arc is extinguished. It results in voltage
oscillation in the line which affects the electrical
equipments.
| Is This Answer Correct ? | 50 Yes | 10 No |
what are smoke detectors ?
4 Answers Indian Military Services,
what is the similarity and difference between ups and inverter?
How to calculate the size of earth cable to earth the neutral of UPS ?
Main CT ration is 400/5, meter CT ratio is open type: -/5A. What is the Multiplying factor of the meter, considering same PT ratio.
What are the properties of a resistor?
If a motor of 30KW rating &200 mtrs distance from feeder give me the cable size selection calculation?
What is the importance of RESONANCE
what is a breaker fail relay
What is the fundamental cause of transients in power system?
What is the amount of no load current of 630 kVA tranformer voltage ratio 11kV/440V ?
What is basic difference between Soft Starters And VFD drives?
Can we connect two or more energy meters/Amp meters on one CT set(Three phase).
5 Answers Parle, Watermark Engineering,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)