in our transmisison sub station why we step down firstly
132kv\33kv then 33kv to 11kv. can we direct step down 132kv
to 11kv.
Answers were Sorted based on User's Feedback
It is only for easy transmission and distribution. 11 kV
is normally used for town distribution. 33kV is used for
transmission to farther areas where the voltage is stepped
down by 33/11 kV sub stations. Normally in 132 incoming sub
stations you will have both 33 kv and 11 kV outgoings
depending upon the location of the 132/33/11 kV sub station.
| Is This Answer Correct ? | 13 Yes | 7 No |
Answer / rakesh verma
1)yes you can directly stapdown 132 kv to 11 kv but in
general cases our transimision outgoing feeder may be
66kv,33kv or 11kv thats why we stap down 132/33/11kv ,if 33
kv not required then we can direct stapdown 132kv to 11kv
2)You can certenly step down the voltage from 132 KV to 11
kv , however in Distribution Substation diffrent level of
voltage comes across so as in your case your substation
should have a diffrent outgoin feeders of 33 kv so your
distribution is 132KV / 33 KV / 11 KV...
3)It is only for easy transmission and distribution. 11 kV
is normally used for town distribution. 33kV is used for
transmission to farther areas where the voltage is stepped
down by 33/11 kV sub stations. Normally in 132 incoming sub
stations you will have both 33 kv and 11 kV outgoings
depending upon the location of the 132/33/11 kV sub station.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / manish
Yes you can directly stapdown 132 kv to 11 kv but in
general cases our transimision outgoing feeder may be
66kv,33kv or 11kv thats why we stap down 132/33/11kv ,if 33
kv not required then we can direct stapdown 132kv to 11kv
| Is This Answer Correct ? | 1 Yes | 2 No |
Dear Mottaleb
You can certenly step down the voltage from 132 KV to 11
kv , however in Distribution Substation diffrent level of
voltage comes across so as in your case your substation
should have a diffrent outgoin feeders of 33 kv so your
distribution is 132KV / 33 KV / 11 KV...
| Is This Answer Correct ? | 2 Yes | 4 No |
What is the diff. between two phase & three phase supply.
How much current in 100 kva Transformer HT & LT side
what is interpose? where it is used and why it is used?
What is difference between YNyn0 and YNyn ??
A motor works on 30kw.it is working on 440volts.How much amper will be Required?
what is auxilliary transformer??
WHAT IS REACTIVE POWER?
What do you mean by cold shinkable cable joint.How it is done.
Why should be the frequency 50 hz 60hz only why not others like 45, 95 56 or anything , why should we maintain the frequency constant if so why it is only 50 hz 60hz?
1.why ACB is not connected in HT side what Happens? 2.how much voltage maintained in ACB breaker? 3.OLTC is connected in primary side in case secondary side connected what happened?
if there is a voltage difference between neutral and earth when we operate any instrument for fraction of time then where is problem?
how we can produce negative DC voltage ? please explain it .,thank u
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)