Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how much load should be given on 5 mva transformer

Answers were Sorted based on User's Feedback



how much load should be given on 5 mva transformer..

Answer / srikanthgss

I think ... since its a 5 MVA transformer , you can have a
unity pf load of 5kw or 4.5mw at 0.9 pf lag or 4.0mw load at
0.8 pf lag .

{ P=VIcos@
Given VI= 5MVA

=> at 0.9pf = 5*0.9=4.5MW
at 0.8pf = 5*0.8=4.0MW
..... etc .
}

Is This Answer Correct ?    75 Yes 7 No

how much load should be given on 5 mva transformer..

Answer / javad

Transformer have an interesting characteristics ie
You can Load the transformer around 20 % of Full load to
around 120% of full load without any problems(At that time
efficiency lie between 75 to 95 %).But maximum
efficiency will give when copper loss equal to core loss that
is around 80 to 85 % of full load.just see load vs efficiency
curve, then u ll b more clear.

Is This Answer Correct ?    51 Yes 10 No

how much load should be given on 5 mva transformer..

Answer / dharmendra

(
Load calculation for 3 phase ac motor



A = 1000 × P(kW) / (√3 × PF × VL-L(V)

Is This Answer Correct ?    3 Yes 1 No

how much load should be given on 5 mva transformer..

Answer / k.sri405

MVA is the apparent power means combination of active and
reactive power. Load means active power so 5 MVA capacity
means we can load this transformer below 5 mw.if there is a
completely resistive load than it may be loaded upto 5 mw
but practically it is not possible.

Is This Answer Correct ?    5 Yes 4 No

how much load should be given on 5 mva transformer..

Answer / ramesh

KW = KVA x pf
1mva=1000kva
kva*0.8= kw
5*0.8=4kw
1kw= 1000W
4=1000*4=4000kw
5mva= 4mw or4000w
--RAMESH

Is This Answer Correct ?    6 Yes 5 No

how much load should be given on 5 mva transformer..

Answer / addicted to know electrical

Load means current,not Mw(power).So,by looking at
P=VI*p.f....
Since i is load which is always variable....the power drawn
from the transformer will always vary......and hence it is
not inour hand how much load shall be given to the
transformer but the efficiency will be max. when load is
equal to iron loss divided by square of secondary
resistance.

Is This Answer Correct ?    2 Yes 23 No

how much load should be given on 5 mva transformer..

Answer / guest

50ohm

Is This Answer Correct ?    4 Yes 49 No

Post New Answer

More Electrical Engineering Interview Questions

how many amps in 1 KVA? V=440v, PF=0.8 and FREQ=50Hz

22 Answers  


What is the importance of earthing?

0 Answers  


In 3 phase induction motor 1hp current rating is 1.5 amps constant ? is correct or not ?

4 Answers   TATA,


What is the principle of Excitation.

1 Answers  


Where earth point should provided in Ships or Submirines.

2 Answers   SSC,


why our power production in multiples of 11.

2 Answers   ABB, Infosys,


i am having a 3 phase 12.5HP motor,that is connected in Star/delta.Without any Trip that motor stopped suddenly why?

8 Answers  


what is the effect of connecting three phase supply lines to three phase auto transformer output terminals through a fuse of 10Amp and a circuit breaker (MCB). Is this connection permanently destroy the transformer?

1 Answers  


what is load flow?

2 Answers  


we have two generators different capacity on 15 MW and other 6MW at 11 KV , 15 MW gen. bus short level current 40KA,and 6MW short level current 25KA,, length of cable 100MTR between 6 MW from 15MW gen. for bus coupling . kindly tell any one can we use both NGR OR one NGR from any GEN. BOTH NGR has diff. rating. Tariq pakistan

0 Answers   RYK Mills,


What will be the voltage regulation of a full load and 0.80 power factor lagging load transformer when a two winding single phase transformer has a voltage regulation of 4.5% at full load and unity power factor?

0 Answers   HPCL,


why the pressure coil is not present in the three phase wattmeter?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)