Answer / srikanthgss
I think ... since its a 5 MVA transformer , you can have a
unity pf load of 5kw or 4.5mw at 0.9 pf lag or 4.0mw load at
0.8 pf lag .
{ P=VIcos@
Given VI= 5MVA
=> at 0.9pf = 5*0.9=4.5MW
at 0.8pf = 5*0.8=4.0MW
..... etc .
}
| Is This Answer Correct ? | 75 Yes | 7 No |
Transformer have an interesting characteristics ie
You can Load the transformer around 20 % of Full load to
around 120% of full load without any problems(At that time
efficiency lie between 75 to 95 %).But maximum
efficiency will give when copper loss equal to core loss that
is around 80 to 85 % of full load.just see load vs efficiency
curve, then u ll b more clear.
| Is This Answer Correct ? | 51 Yes | 10 No |
Answer / dharmendra
(
Load calculation for 3 phase ac motor
A = 1000 × P(kW) / (√3 × PF × VL-L(V)
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / k.sri405
MVA is the apparent power means combination of active and
reactive power. Load means active power so 5 MVA capacity
means we can load this transformer below 5 mw.if there is a
completely resistive load than it may be loaded upto 5 mw
but practically it is not possible.
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / ramesh
KW = KVA x pf
1mva=1000kva
kva*0.8= kw
5*0.8=4kw
1kw= 1000W
4=1000*4=4000kw
5mva= 4mw or4000w
--RAMESH
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / addicted to know electrical
Load means current,not Mw(power).So,by looking at
P=VI*p.f....
Since i is load which is always variable....the power drawn
from the transformer will always vary......and hence it is
not inour hand how much load shall be given to the
transformer but the efficiency will be max. when load is
equal to iron loss divided by square of secondary
resistance.
| Is This Answer Correct ? | 2 Yes | 23 No |
how many amps in 1 KVA? V=440v, PF=0.8 and FREQ=50Hz
What is the importance of earthing?
In 3 phase induction motor 1hp current rating is 1.5 amps constant ? is correct or not ?
What is the principle of Excitation.
Where earth point should provided in Ships or Submirines.
why our power production in multiples of 11.
i am having a 3 phase 12.5HP motor,that is connected in Star/delta.Without any Trip that motor stopped suddenly why?
what is the effect of connecting three phase supply lines to three phase auto transformer output terminals through a fuse of 10Amp and a circuit breaker (MCB). Is this connection permanently destroy the transformer?
what is load flow?
we have two generators different capacity on 15 MW and other 6MW at 11 KV , 15 MW gen. bus short level current 40KA,and 6MW short level current 25KA,, length of cable 100MTR between 6 MW from 15MW gen. for bus coupling . kindly tell any one can we use both NGR OR one NGR from any GEN. BOTH NGR has diff. rating. Tariq pakistan
What will be the voltage regulation of a full load and 0.80 power factor lagging load transformer when a two winding single phase transformer has a voltage regulation of 4.5% at full load and unity power factor?
why the pressure coil is not present in the three phase wattmeter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)