Answer / srikanthgss
I think ... since its a 5 MVA transformer , you can have a
unity pf load of 5kw or 4.5mw at 0.9 pf lag or 4.0mw load at
0.8 pf lag .
{ P=VIcos@
Given VI= 5MVA
=> at 0.9pf = 5*0.9=4.5MW
at 0.8pf = 5*0.8=4.0MW
..... etc .
}
| Is This Answer Correct ? | 75 Yes | 7 No |
Transformer have an interesting characteristics ie
You can Load the transformer around 20 % of Full load to
around 120% of full load without any problems(At that time
efficiency lie between 75 to 95 %).But maximum
efficiency will give when copper loss equal to core loss that
is around 80 to 85 % of full load.just see load vs efficiency
curve, then u ll b more clear.
| Is This Answer Correct ? | 51 Yes | 10 No |
Answer / dharmendra
(
Load calculation for 3 phase ac motor
A = 1000 × P(kW) / (√3 × PF × VL-L(V)
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / k.sri405
MVA is the apparent power means combination of active and
reactive power. Load means active power so 5 MVA capacity
means we can load this transformer below 5 mw.if there is a
completely resistive load than it may be loaded upto 5 mw
but practically it is not possible.
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / ramesh
KW = KVA x pf
1mva=1000kva
kva*0.8= kw
5*0.8=4kw
1kw= 1000W
4=1000*4=4000kw
5mva= 4mw or4000w
--RAMESH
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / addicted to know electrical
Load means current,not Mw(power).So,by looking at
P=VI*p.f....
Since i is load which is always variable....the power drawn
from the transformer will always vary......and hence it is
not inour hand how much load shall be given to the
transformer but the efficiency will be max. when load is
equal to iron loss divided by square of secondary
resistance.
| Is This Answer Correct ? | 2 Yes | 23 No |
What is servo Motor? What's the advantages of this motor over Induction motor?
tan delta test of current transformer.
what is the difference between direct loading and indirect loading?
A three phase transformer 460v primary 220v secondary (three phase four wire system.) Why did we get 460 volts across the neutral on the secondary side?
why should small green grass ans small plant should not be there inside the transformer Yard in the factories
which type of motor we are using in local train???
4 Answers Asia MotorWorks AMW,
what is the minimum dielectric stregth of transformer oil.
FACP Means
Circuit diagram of tube light without starter using electrical choke
What is the technical difference between IS:1554 and Indian Railway IRS:S63/2007
Why Utility Distribution System in India is mainly at 11 kV? Why not Utility go for 33 kV?
how to select DG set for certain load?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)