i have one transformer 1000kva, 11/.433kv. we are using
200/5 amp. ct unit for measuring purpose, & one 800 amp.
V.C.B Unit for the same t/f operate, i wants to known the primary
current of T/F is only 53 amp. why we used 800 amp.
V.C.B ? & 200/5 amp. CT Unit.
Answer Posted / vinit patil
You are right, you should fight with your electricity board
regarding the HT Metering CT ratio. You should actually
required 100/5 ratio.
But while deasigning VCB it is always prfarable to go on
higher side because it can sustain the heavy short circuit
current. One thing should be noticed that the protection
CTs should be as per the Primary current of the ransformer.
| Is This Answer Correct ? | 5 Yes | 2 No |
Post New Answer View All Answers
What is the effect of interchanging core(made of steel) and winding(made of copper) material in case of transformer? Give proper explanation in regard to different losses in transformer.
How one may guess the direction from which the distribution line is incoming if there is no pole plate on poles?
What is the function of interposing current transformer?
Whats the difference btwn a latch, port,data bus buffer? Do they all not hold data in d flip flops??
How to calculate cable size by using load.?? Any formula...
what is the benefit of floating our DC source? if i have two floating DC source of which 1 has a ref voltage of -21VDC and the other of -18VDC. can it be connected in parallel to share a common ref voltage? if not, how do i make both sources to be of common ref voltage? tks
Name the test signals used in control system
What is pole of the system?
What are the main significances of root locus?
How to calculate flow of water delivered by pump when pressure & size of pipe line is given
If 22 KV HT line, Current transformer is 25/5 then how to calculate multiplying factor.
why don't we use the generator as a motor? and what will happen?
What is the difference between isolators and electrical circuit breakers? What is bus-bar?
what is control supply rating of a machine
Mention what are the different colors on wires indicates?