How to calculate HV Cable Sizing & what are the factors to be considered for selection?...

Answer / ashish tiwari

The HV cbale size shall be base on the fault level on HV
side. Like 18.4KA fault current for 11 KV supply & 21.34 KA
fault current for 33 KV supply. We can calculate the HV
cable
BY USING FORMULA ISH = K x A/( sq. root of T)


Where,
ISH :SHORT CIRCUIT CURRENT IN KA (r.m.s.)

T :DURATION OF SHORT CIRCUIT CURRENT IN SECONDS

A :AREA OF ALUMINIUM CONDUCTOR IN MM2

K :IS A CONSTANT = 0.094 for aluminium

ISH x Sq.rootT 18.4 x Sq. root 1
A = ------------ = ------------
K 0.094
= 195.7 sq.mm

HENCE 3 C x 240 SQ.MM XLPE (AL) CABLE IS REQUIRED FOR
INCOMING SIDE AS WELL AS OUTGOING SIDE OF 11 KV SUPPLY.

Is This Answer Correct ?    32 Yes 19 No

How to calculate HV Cable Sizing & what are the factors to be considered for selection?...

Answer / ali

i want calcuiate the size of hv 6.6kv cable can trans 750 amper

with regard

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

What will happen if the field of synchronous generator is removed when it is in operation with no load?

3 Answers   HJ, UPPCL,


How do you commission a power Transformer?

1 Answers   EEI,


how can i increase the excitation on full load running engine??

1 Answers  


What is the Temperature to be set in Thermostat provided in Marshalling box of the Transformer / Motor.

0 Answers   Kirloskar,


what is the difference between the electrical and electronic choke?

1 Answers  






I have 10 amp MCB for my air conditioner of 1.5 ton capacity. When I connect the ac direct it is started running but when connected through stabliser the Mcb Get trip and air conditioner couldn't start.please confirm whether Mcb is required to be upgraded to 20 amp. There is no fault in ac and the stabliser. Please advice the reason of tripping the mcb when connected through the stabliser.

1 Answers  


Difference in load break switch, isolator and circuit breaker.

1 Answers   KSEB, L&T, Siemens,


IS THE ANY DIFFERENCE B/W GENERATORS & ALTERNATORS

6 Answers  


defination of lines

0 Answers  


What is the power requirement of tamil nadu for one month?

0 Answers  


my bachelors was done with EEE now i got admit in NU with CS as course. how to answer this qns 1) why u choose cs? 2) why u changed from eee to cs

0 Answers  


what efficiency of transformer at 100% load

0 Answers   Emerson,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)