How to calculate HV Cable Sizing & what are the factors to
be considered for selection?.
Answers were Sorted based on User's Feedback
Answer / ashish tiwari
The HV cbale size shall be base on the fault level on HV
side. Like 18.4KA fault current for 11 KV supply & 21.34 KA
fault current for 33 KV supply. We can calculate the HV
cable
BY USING FORMULA ISH = K x A/( sq. root of T)
Where,
ISH :SHORT CIRCUIT CURRENT IN KA (r.m.s.)
T :DURATION OF SHORT CIRCUIT CURRENT IN SECONDS
A :AREA OF ALUMINIUM CONDUCTOR IN MM2
K :IS A CONSTANT = 0.094 for aluminium
ISH x Sq.rootT 18.4 x Sq. root 1
A = ------------ = ------------
K 0.094
= 195.7 sq.mm
HENCE 3 C x 240 SQ.MM XLPE (AL) CABLE IS REQUIRED FOR
INCOMING SIDE AS WELL AS OUTGOING SIDE OF 11 KV SUPPLY.
Is This Answer Correct ? | 32 Yes | 19 No |
Answer / ali
i want calcuiate the size of hv 6.6kv cable can trans 750 amper
with regard
Is This Answer Correct ? | 0 Yes | 0 No |
What will happen if the field of synchronous generator is removed when it is in operation with no load?
How do you commission a power Transformer?
how can i increase the excitation on full load running engine??
What is the Temperature to be set in Thermostat provided in Marshalling box of the Transformer / Motor.
what is the difference between the electrical and electronic choke?
I have 10 amp MCB for my air conditioner of 1.5 ton capacity. When I connect the ac direct it is started running but when connected through stabliser the Mcb Get trip and air conditioner couldn't start.please confirm whether Mcb is required to be upgraded to 20 amp. There is no fault in ac and the stabliser. Please advice the reason of tripping the mcb when connected through the stabliser.
Difference in load break switch, isolator and circuit breaker.
IS THE ANY DIFFERENCE B/W GENERATORS & ALTERNATORS
defination of lines
What is the power requirement of tamil nadu for one month?
my bachelors was done with EEE now i got admit in NU with CS as course. how to answer this qns 1) why u choose cs? 2) why u changed from eee to cs
what efficiency of transformer at 100% load