what is the difference between the megger and multimeter
operation ?
Answers were Sorted based on User's Feedback
Answer / ajay
megger is used to measure insulation resistance.multimeter is used to measure coil resistance
Is This Answer Correct ? | 37 Yes | 4 No |
Answer / raghavendran
The working mechanism of a Meggar and a Multimeter with
regard to measuring a resistance is the same.In this case
Voltage is applied across the body whose resistance is to be
measured.
1)for meggar, there will be two coils namely 'control coil'
and 'deflection coil'.The 'Control Coil' will always be kept
energized by the DC Source.If the insulation strength is low
then there will be current flow through the 'deflection
coil' and the resulting torque in the coil will produce
deviation in the pointer connected to a permanent magnet.The
torque produced by the two coils will be opposite in nature.
2)for multimeter,the control coil will be replaced by a
spring whose tension tends to keep the pointer in one
direction.when current flows through the deflecting coil (ie
when weak insulation)a torque, opposite to the tension of
the spring is produced tending to move the pointer in other
direction.thus showing the corresponding Ohmic Value.
Is This Answer Correct ? | 33 Yes | 2 No |
Answer / pillay
meggar is actually a brand name, but it is more often than
not associated with with insulation resistance testers.The
meggar tester /or insulation tester actually uses a high
voltage at its terminals to do the measurements thus being
more efficient in driving In a current and than the
measurements are made.
Multimeter as the name says is used for a variety of
measurements but using basically the same moving coil.when a
high resistance or very small leakage is to be tested using
a multimeter it usually fails because of its in ability to
drive a current through a very high resistance circuit and
give a correct reading.
I would always use a MEGGAR tester for insulation testing
and a multimeter for other testing.
Is This Answer Correct ? | 24 Yes | 7 No |
what is bus coupler, where it used.
why we use 630mm single core cable for transformer secondary side and why two neutral cable
What are eddy current and define rms value?
WHAT IS LINIER MOTOR?
The rating of Transformer are 11KV, 22KV, 33KV instead of 10KV, 20KV & 30KV?
What is a soft start?
i am BSEE student, my project study is to synchronize the generator of an hospital, it have a one 313KVA standby-power diesel gen.,and three 100kva transformer.The generator system is operated manually and no ATS or UPS. one more new building is being build so the transformer will be upgrade to a higher vale. 1)how i can connect the new gen. to the old gen. and to the synchronize panel? 2)what is the new gen. to be buy?(rating, etc.) These is my title: To synchronize the generator system of the ____ Hospital. Anyone have a good title? Thanks.
what is phase shifting transformer.
explain transformer ct connection?
IN WHICH MODE THE TRANSFORMER WILL GET A MAXIMUM OUT PUT VOLTAGE. ASKED FOR POWER GRID EXAMINATION STAT-STAR,STAR-DELTA,DELTA-STAR,DELTA-DELTA
how to fit 3 HP crompton gear motor with conveyor with the use of staring delta starter or ordinary starter?
if current required for triggering thyristor at -30 degrees(temp) is 80 mA, what is the current required at 60 degrees