What is the diffrence in between Class PS & Class 5P10 for
CTs
Answers were Sorted based on User's Feedback
Answer / subharaj
PS Class CTs are used for Differential protection & 5P10
are used for other protection.
| Is This Answer Correct ? | 18 Yes | 0 No |
Answer / k. sankaraiah
calss 5p10 used for normal protection, but PS class used
for special protection. 5p10 is used for non balance
circuits but PS class used for balance circuit.where ever
circulating current is balanced at that time only Ps class
using.This can be used only two CTs are present. Ex.
Differential protection & REF.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / k.prakashchandra
5P10 ct belongs to PS ct group,being specified
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jonnalagadda chowdary
PS Class CTs are used for Differential,over current
protection(direct protection) & 5P10 are used for restricted
earth fault(indirect protection)
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / fikizolo
Theres basicly no difference, they both overcurrent protection CT's
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / chirag
class ps ct's are special class ct's which are used in
protection where high accuracy is required other than that
5p10 are used.accuracy of 5p10 is less than class ps ct's.
| Is This Answer Correct ? | 2 Yes | 7 No |
Answer / satya dev
Class PS CTs are used for Metering system & Class 5P10 used
for Protection
| Is This Answer Correct ? | 1 Yes | 19 No |
If we have 11 kv RYB Phase single core cable near about. Then wht effect and losses
Why lightning arrester blast in rainy day?
1 Answers Eco Cement, Mahaveer, MBDL,
what is the mager value of star motor and delta motor between phase to ground and phase to phase, and minimum how much should be value ?
hai now i am working as a electrical design engineer in construction field can i get a job in oil and gass field or power plant project as a electrical design engineer?
Why transformer used in UPS??
How to calculate Temp from Resister from PT100 equation,
We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Suppose we have long 2 core DC cables running from our DCDB in control room to the load (length of around 2 to 3 km). Do we need to protect these long DC cables from earth leakages or not? If yes how?
Hi, We have have the major losses between BBT ( Bus Bar Trunking) to LT Incomer & LT to HT incomer, how to arrive the losses?
what is RR number Abbreviation energy meter
what is the difference between contactors & relay.
What is the meaning of C1, C61, C91 cable
why are installed water leakage detection system data centers & server rooms
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)