Answer / subharaj
PS Class CTs are used for Differential protection & 5P10
are used for other protection.
| Is This Answer Correct ? | 18 Yes | 0 No |
Answer / k. sankaraiah
calss 5p10 used for normal protection, but PS class used
for special protection. 5p10 is used for non balance
circuits but PS class used for balance circuit.where ever
circulating current is balanced at that time only Ps class
using.This can be used only two CTs are present. Ex.
Differential protection & REF.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / k.prakashchandra
5P10 ct belongs to PS ct group,being specified
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jonnalagadda chowdary
PS Class CTs are used for Differential,over current
protection(direct protection) & 5P10 are used for restricted
earth fault(indirect protection)
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / fikizolo
Theres basicly no difference, they both overcurrent protection CT's
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / chirag
class ps ct's are special class ct's which are used in
protection where high accuracy is required other than that
5p10 are used.accuracy of 5p10 is less than class ps ct's.
| Is This Answer Correct ? | 2 Yes | 7 No |
Answer / satya dev
Class PS CTs are used for Metering system & Class 5P10 used
for Protection
| Is This Answer Correct ? | 1 Yes | 19 No |
why current is denoted by I
I NEED RRB CHENNAI (JE ELECTRICAL) QUESTION PAPER FOR LAST 5 YEAR AND I NEED RRB (JE ELECTRICAL) SYLLABUS.PLEASE SEND MY E-MAIL joo28_eee@yahoo.co.in
12 Answers DFM, Hindustan Unilever Limited, JE, Pace, RRB,
what are the units of cable insulation?
How will you calaculate the Ct ratio based on connected load 500KVA,and 11KV supply ?
Can we use a window type neutral CT instead of a bar type neutral CT. We have an issue with a neutral bar type CT of 800/1 ratio with a Circuit breaker NS800L shneider type, and we want to change it with a window type. Pls advise. Thanks
what is post close & pre close of trip circuit supervision relay in circuit breaker control scheme?
Two bulbs of 100w and 40w respectively connected in series across a 230v supply which bulb will glow bright and why?
What do you mean by S.F.U. unit? application of it.
what is the difference between a race around condition and toggling?
please tell 1 ton equal to how many kilo watt?? in some converter software's that is 3.5 kw. is it right?
what is the meaning of WYE and DELTA in Electric meter?
how i sync. the different size of generator.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)