What is the diffrence in between Class PS & Class 5P10 for
CTs
Answer Posted / subharaj
PS Class CTs are used for Differential protection & 5P10
are used for other protection.
| Is This Answer Correct ? | 18 Yes | 0 No |
Post New Answer View All Answers
Explain M Var? Which types of problem occurs when reactive power increase at the time of full load of plant and at the time of synchronize of plant?
what happen when power factor of 2 parallely operated transformer become equle?
Define average demand?
what is the meaning of 0.5ohm Resistance
can anybody tell me that for p.f. Improvment we use capacitor banks but how to decide its capacitance. As we all know how to calculate kvar but what abt capacitance value
How do we calculate the Out put voltage of generator, after the excitation is being given?
what is EIB lighting control system? what is the advantages of this system?
in HT service 3ph 4 wire service Y-phase voltage shows zero . whether it is meter fault? or what be the reason ? if y-ph voltage zero ,can current is recorded? reasons for failure?
Can you explain about pole discrepancy scheme
How to do stting of vl250 siemens MCCB
HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT-SWITCH BOARD,MLDB,ACB,BUSBAR,ETC,......?
hi frenz,its aswathy.i hve aplied for the hpcl test on feb,pls send the test patern & the placement papers as soon as possible. mail-id :kjaswathy@gmail.com
what is the current density of copper & alluminium.
what is the minimum voltage require to injure our body?
explain with diagram how to protect transformers and substations from over current with help of CT's?