Answer / rahul sr
Passive Loop: The transducer must be provided by an
external power supply for its working. Then it generates
the signal according to the Process parameter. This may
have either 2 wires, 3 wires or 4 wires.
Active Loop: There is no need to give external power supply
for the transducer. The sensor itself generates signal
without giving power supply. This will have only 2 wires.
| Is This Answer Correct ? | 40 Yes | 22 No |
Answer / anatoli
Active input - loop is powered from card/module
Passive input - loop is powered from external source
Output loops are always active.
Number of wires is irrelevant
| Is This Answer Correct ? | 13 Yes | 2 No |
Answer / ali
Kindly check the data sheet of Stahl Transmitter Supply Unit
Field Circuit Ex i
Series 9160
and check 9160/13-10-11 as passive O/P & 9160/13-11-11 as active O/P .
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ali
If we consider temperature sensors for example , active sensors are like LM35 -3 wires, need supply - thermocouples 2 wires -don't need supply , but both of them give mV as O/P .
on other hand pt100 can't gives O/P voltage or current with or without supply .
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / ram
Passive Loop : Two wired loop powered . It is consuming the
power and generates the signal acoording to the process
parameter values or inputs.
Active Loop : External Power supply or separate power
supply and Signals generates either two wire or four wire
concept.
| Is This Answer Correct ? | 11 Yes | 13 No |
what is formula for calculating flow if i have pressure and pipe diameter?
How would you choose differential range?
I wnat to practice more online type questions .so will you show them me to take a practice test?
what is modbus & what signals are taken through it
How can we use feedback signal frm rtd for monitoring and in dcs for controlling ,then which type of rtd is sutaible 2 , 3,4wire and why ?
what is PID n give me brief info. about P&I&D.
䑰ҕ䔈ҕ䖠ҕ䘰ҕ䛀ҕ䝐ҕ䟐ҕ䢐ҕ䥐ҕŹ
can install leveltrol in steam drum for measurment the level of steam drum? if not then why?
What are difference between automatic and manual control system?
tell me the field & lab calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter, temperature transmitter, temperature indicator, flow indicator, level indicator, control valve, thermocouple, pressure indicator (digital & analogue),
Displace type LT to be calibrated in workshop, wt. 40, dia- 60 mm, density- 0.8kg/cm3.
Why we are using sqare root in flow?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)